mont1230
Member
I have a question regarding the 2009 IECC. In Table 405.5.2(1) page 35 it has a column for Standard and proposed design. In the Standard Reference design is for the prescriptive method and the proposed design for the performance method? When a house is done by Prescriptive method and when getting back the blower door results and calculating by the (standard reference design) specific leakage area it passes. The question is that most HERS and BPI raters are running a REMrate software and the natural ACH always comes in failing. Which results in more cfm's and costing more money and makes no since by doing a code by a prescriptive method. The raters do not need to run a REMrate software to do a prescriptive method? But why will it pass by the standard method, but not the Proposed design method? Can you give me an explanation between the two. For example if I took a 2500 square feet house and built it to the prescriptive method, should the house always pass if the blower test result is 7 ACH or less and that the specific leakage area passes too? But if I took the same house and did the performance method which usually requires less insulation requirements and passes the blower door test but always comes up failing in the minimum natural ACH of 0.35. How can this house that in most cases built in prescriptive method be built tighter than performance but passes. This is very hard to understand. We want to make sure that these houses are being design and built correctly.