• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Pressure treated posts in crawl spaces

Big Mac

Gold Member
Joined
Oct 22, 2009
Messages
563
Per the 2009 IRC Sec. R317.1.4, columns in enclosed crawl spaces or in unexcavated areas located within the periphery of the building when supported by a concrete pier or metal pedestal at a height more than 8 inches do not need to be pressure treated, otherwise, less than that, they will need to be pressure treated.

Is anybody out there calling this besides us?
 
There are different earth to wood separation requirements for various types of materials and different earth to wood separation requirements for posts under the structure and posts outside the structure. I believe the separation requirements for earth to wood at the exterior is 6".

If the pony walls you are refering to under the structure are taking the place of support posts and beams, then they too should be pressure treated if within 8" of the earth.
 
Big Mac said:
If the pony walls you are refering to under the structure are taking the place of support posts and beams, then they too should be pressure treated if within 8" of the earth.
I can find the column requirement in the code but not pony walls in a crawl space. What section are you using?
 
High Desert: Please note I said should, not shall.

Here is some logic that would seem to apply.

1st) columns (posts) on the exterior are permitted to have only a 6" separation from earth, yet columns (posts) under the floor are required to be separated by not less than 8". Section 317.1.4.

2nd) the code requires that pony walls (wood framing members) at the exterior be separated not less than 8" from the exposed ground, unless they are pressure treated. Section 317.1, #2. It doesn't seem logical that pony walls (structural framing members) under the floor would be permitted to be closer than what is required at exterior walls, since the requirement for columns under floor is more restrictive, than for those placed outside.

3rd) when a pony wall is placed below a floor system, it usually replaces not only the posts, but the beam as well. Wood griders closer than 12" from the earth are required to be pressure treated. An argument could be made I suppose to say that the structural wood wall which is acting as a girder replacement should be no less than 12" to earth, unless it is pressure treated.

Yes I know there are other ways to meet materials resistant to decay, but for the most part around here, pressure treated materials are used so that is what I typically reference. In my experience people are rarely willing to pay for those other materials.

Seems logical to me. As I often say, if one were to try and address every possible scenario that could happpen in the code, it would take a truck to carry the code books around. Somewhere logic need sto be applied.

No I cannot give you a specific chapter and verse that says wood walls framed underfloor to replace column and beam construction must be pressure treated when less than 8" from the earth. However, if it gets to be a problem be sure that sooner or later it will be considered as a code amendment. And the book will continue to get bigger and bigger and bigger.
 