One of the biggest complaints by contractors is the inconsistency of inspectors. One of the biggest problems that inspectors face is inconsistency from other inspectors. Here is one example that I would like to elaborate and sort of provide a breakdown of my opinion on the situation.
You arrive at a jobsite for an inspection to perform a service inspection. You notice 2 things right off the bat. 1) There is no intersystem bonding terminal installed and 2) There is only 1 ground rod installed.
So rather than assume these are violations, you politely ask the contractor some questions. 1) I don't see the intersystem bonding terminal. Did you install it inside? and 2) I see you only have 1 ground rod. Is there a CEE connection inside or did you do a resistance check and have <25 ohms of resistance to ground?
Your responses are as follows:
1) What is an intersystem bonding terminal?
2) What do you mean? What is a CEE?
After explaining NEC 250.94 to the contractor, you then tell him that a CEE is a concrete encased electrode and if he already has a connection to one then he did not need the ground rod anyway. If the ground rod and water pipe is the only connection then you need a 2nd rod unless you proved <25 ohms resistance (very expensive meter by the way)
The next response from the contractor is:
"I have installed 20 services this year so far and you are the first one to even mention 250.94 and the ground rod thing. How come inspectors in the other towns don't write these things up?"
And we are off. The electrician either does not know his job or knows what they can get away with in other towns and wants to try it in this one now too. I can only assume that the other inspectors are either not actually performing the inspections, don't know the requirements themselves or take it upon themselves to intentionally remove that code section because of their personal opinion. The last one is the one that pretty much causes lots of problems although all the reasons are scary.
So now the next thing out of the contractor's mouth is:
"All of you guys have different interpretations for these gray areas"
?????????????? WTF over???? What gray area are we talking about here. There are some gray areas of the NEC and for sure there are 2 very specific areas that are subjective to the inspector but these items are pretty rock solid black and white.
So as inspectors I thin we have to:
1) Try to use as much objectivity as possible as the code is written.
2) Take into consideration the "intent" of the code when grayish.
3) Leave the personal opinions at home before you come to work.
4) Realize that we are not perfect and listen when challenged. You may learn something.
5) Be consistent with everyone. Fair and consistent is the key.
Thoughts on this one?
You arrive at a jobsite for an inspection to perform a service inspection. You notice 2 things right off the bat. 1) There is no intersystem bonding terminal installed and 2) There is only 1 ground rod installed.
So rather than assume these are violations, you politely ask the contractor some questions. 1) I don't see the intersystem bonding terminal. Did you install it inside? and 2) I see you only have 1 ground rod. Is there a CEE connection inside or did you do a resistance check and have <25 ohms of resistance to ground?
Your responses are as follows:
1) What is an intersystem bonding terminal?
2) What do you mean? What is a CEE?
After explaining NEC 250.94 to the contractor, you then tell him that a CEE is a concrete encased electrode and if he already has a connection to one then he did not need the ground rod anyway. If the ground rod and water pipe is the only connection then you need a 2nd rod unless you proved <25 ohms resistance (very expensive meter by the way)
The next response from the contractor is:
"I have installed 20 services this year so far and you are the first one to even mention 250.94 and the ground rod thing. How come inspectors in the other towns don't write these things up?"
And we are off. The electrician either does not know his job or knows what they can get away with in other towns and wants to try it in this one now too. I can only assume that the other inspectors are either not actually performing the inspections, don't know the requirements themselves or take it upon themselves to intentionally remove that code section because of their personal opinion. The last one is the one that pretty much causes lots of problems although all the reasons are scary.
So now the next thing out of the contractor's mouth is:
"All of you guys have different interpretations for these gray areas"
?????????????? WTF over???? What gray area are we talking about here. There are some gray areas of the NEC and for sure there are 2 very specific areas that are subjective to the inspector but these items are pretty rock solid black and white.
So as inspectors I thin we have to:
1) Try to use as much objectivity as possible as the code is written.
2) Take into consideration the "intent" of the code when grayish.
3) Leave the personal opinions at home before you come to work.
4) Realize that we are not perfect and listen when challenged. You may learn something.
5) Be consistent with everyone. Fair and consistent is the key.
Thoughts on this one?