Hello, I will try to make this concise. I searched the topics and didn't see this. Hopefully you guys can help.
2006 IBC used, M occupancy, type 5A (to allow 2 stories).
5A requires 1hr construction (all elements per table 601).
One wall is 5.5 feet from a property line. All others are 20+ feet.
Because the "fire separation distance" is greater than 5 feet, per 704.5 the 1hr rating can be for exposure from the inside. (correct me if i am wrong up until now.)
704.2 "projections" spells out how far the eve overhangs can project. In this case, they project 2 feet, or to a point 3.5 feet from the lot line. Based on 704.2, this is allowable.
The question becomes, refering to 704.2.3 "combustible projections". this is the requirement for 1hr fire rated const, when located where openings are not permitted (less than 3' fire sep.distance), or where they are required to be protected (3-5 ft fire sep dist)(per 704.8).
MY questions: Is this refering to the fire separation distance of the wall, or the actual projection its self?? You would have a wall protected on the inside and the ceiling protecting the roof framing from the underside. Do you need to protect the eves, that are 3'6" from the lot line? Then the next question is, what if those eves have soffit venting?? is that considered an "unprotected opening" in something that is required to be protected??
Thanks in advance for opinions and expertiese.
2006 IBC used, M occupancy, type 5A (to allow 2 stories).
5A requires 1hr construction (all elements per table 601).
One wall is 5.5 feet from a property line. All others are 20+ feet.
Because the "fire separation distance" is greater than 5 feet, per 704.5 the 1hr rating can be for exposure from the inside. (correct me if i am wrong up until now.)
704.2 "projections" spells out how far the eve overhangs can project. In this case, they project 2 feet, or to a point 3.5 feet from the lot line. Based on 704.2, this is allowable.
The question becomes, refering to 704.2.3 "combustible projections". this is the requirement for 1hr fire rated const, when located where openings are not permitted (less than 3' fire sep.distance), or where they are required to be protected (3-5 ft fire sep dist)(per 704.8).
MY questions: Is this refering to the fire separation distance of the wall, or the actual projection its self?? You would have a wall protected on the inside and the ceiling protecting the roof framing from the underside. Do you need to protect the eves, that are 3'6" from the lot line? Then the next question is, what if those eves have soffit venting?? is that considered an "unprotected opening" in something that is required to be protected??
Thanks in advance for opinions and expertiese.