Maybe I have been over-stepping. I have always required some method to protect condensate traps from freezing, and have never been challenged until now. The mechanical engineer has responded to my request by claiming that IPC 1002.7 does not apply. However, upon a close reading I am not so sure. For an RTU with a trap required by the MFR, if it freezes the trap seal will be lost and the unit may not perform, but is this code if the MFR doesn't require it? I always leaned on the fact that the IMC said that condensate drainage had to comply with the IPC, but I am just now noticing that only applies to "joints and connections" per IMC 307.2.2. Have I been wrong all along or have I just forgotten where I came up with this?