jar546
CBO
Scenario:You have a residential dryer on the top floor of a building. The roof is a 1-hour rated concrete structure. The dryer duct is 4-inch steel and will route directly from the dryer through the roof. The plan is to wrap the dryer duct with 1-hour rated duct wrap and route it up through the roof without a fire damper.
Question: Does wrapping the dryer duct with rated wrap qualify as an acceptable enclosure for exception #1 of 2015 IMC Section 607.6.1 for ducts located in the cavity of a wall?
Opinion: This opinion also applies to the 2018, 2021, and 2024 IMC.
2015 IMC Section 607.6 is not applicable in this case. This section addresses the penetration of a ceiling membrane of a roof/ceiling assembly and not a fire-resistant rated concrete surface.
For a residential dryer venting through a fire-resistant rated concrete roof, the ductwork must meet the minimum thickness requirements specified in Section 603.4. Section 504.2 requires clothes dryer ducts to be constructed of galvanized steel or aluminum of the thickness specified in Section 603.4. Additionally, the minimum thickness requirement of Section 504.8.1 applies if the dryer is a residential dryer.
It is important to note that the annular space provision of Section 504.2 does not apply to this condition because it applies when the ceiling membrane of a roof/ceiling assembly is penetrated, not when a fire-resistance rated concrete deck is penetrated.
Question: Does wrapping the dryer duct with rated wrap qualify as an acceptable enclosure for exception #1 of 2015 IMC Section 607.6.1 for ducts located in the cavity of a wall?
Opinion: This opinion also applies to the 2018, 2021, and 2024 IMC.
2015 IMC Section 607.6 is not applicable in this case. This section addresses the penetration of a ceiling membrane of a roof/ceiling assembly and not a fire-resistant rated concrete surface.
For a residential dryer venting through a fire-resistant rated concrete roof, the ductwork must meet the minimum thickness requirements specified in Section 603.4. Section 504.2 requires clothes dryer ducts to be constructed of galvanized steel or aluminum of the thickness specified in Section 603.4. Additionally, the minimum thickness requirement of Section 504.8.1 applies if the dryer is a residential dryer.
It is important to note that the annular space provision of Section 504.2 does not apply to this condition because it applies when the ceiling membrane of a roof/ceiling assembly is penetrated, not when a fire-resistance rated concrete deck is penetrated.