Inspector 102
REGISTERED
Where the space above the ceiling is used as return air, how should the PCV piping or pex water lines be protected?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
By not using PVC and instead use CPVC if possible or copper.Where the space above the ceiling is used as return air, how should the PCV piping or pex water lines be protected?
Commercial. Should have been cast iron.Sorry, commercial structure, PVC for waste stack, pex tubing for water distribution. Looks like I need to check the listing on the PEX tubing for UL standard. Thanks for the guidance.
Like you are from Massachusetts....Commercial. Should have been cast iron.
Every commercial construction job that has plumbing in a plenum space uses cast iron. I've even seen it in a new SFR to keep the noise down. Sounds to me like something that was not caught on plan review. Copper is just too expensive right now for DWV.Like you are from Massachusetts....
I've seen copper and cast iron but not CPVC.Commercial. Should have been cast iron.
We see the condensate lines with CPVC in plenum spaces. Larger commercial we see copper.I've seen copper and cast iron but not CPVC.
I hate to give that up entirely, because we are also dancing the line of how much whatever we can put above a dropped ceiling before sprinklers should be installed....But that is irrelavent to plenum or not....Now if your HVAC system meets 606.2.2 is IMC 602.2.1.8 even a concern from a life safety point since the smoke will not be distributed throughout the building?
Just a thought for discussion since the code for materials in a plenum is over 60 years old that I am aware of, and smoke detection has improved dramatically over the last twenty years.
606.2.2 Common supply and return air systems.
Where multiple air-handling systems share common supply or return air ducts or plenums with a combined design capacity greater than 2,000 cfm (0.9 m3/s), the return air system shall be provided with smoke detectors in accordance with Section 606.2.1.
Exception: Individual smoke detectors shall not be required for each fan-powered terminal unit, provided that such units do not have an individual design capacity greater than 2,000 cfm (0.9 m3/s) and will be shut down by activation of one of the following:
1. Smoke detectors required by Sections 606.2.1 and 606.2.3.
2. An approved area smoke detector system located in the return air plenum serving such units.
3. An area smoke detector system as prescribed in the exception to Section 606.2.1.
In all cases, the smoke detectors shall comply with Sections 606.4 and 606.4.1.