Marshal Chris
Silver Member
Hello all,
At least I wont be able to bump a 6 year old thread here.
Anyway, Using NYS "enhancements" of the IBC/IFC, here's my dilemma.
We have a Type V - 4 story - R-1(hotel) under construction.
1) Based upon 506.3 (area increase) , only a NFPA 13 system would be applicable correct? Not a 13R? I'm basing this that 506.3 specifically calls for complinace with 903.3.1.1.
2) We adopt the most recent edition of all NFPA. 07 NFPA 13 8.15.8 allows eliminating sprinkler head in bathrooms 55 square foot or less.
They can get the sprinkler increase without sprinklering the whole building? Is there something I'm missing? It may comply, I just don't agree. Because the second half of this is the vent fans in the bathroom don't have dampers where it penetrates the 2 hr shaft enclosure because they are building it to 716.5.3.1-1(1.1).
716.5.3.1 Penetrations of shaft enclosures. Shaft enclosures that are permitted to be penetrated by ducts and air transfer openings shall be protected with approved fire and smoke dampers installed in accordance with their listing. Exceptions:
1. Fire dampers are not required at penetrations of shafts where:
1.1. Steel exhaust subducts are extended at least 22 inches (559 mm) vertically in exhaust shafts, provided there is a continuous airflow upward to the outside;