phuzzy phil
Registered User
With a two-story Type VB, R-2, egress balcony with a roof/floor ceiling, does 2018-IBC Section 903.3.1.2.1-2 NFPA 13R-Balconies, Decks, Open Corridors require sprinkling? I thought it was applicable at the 2nd story egress balcony at a minimum during my plan review. Sprinkler Contractor and Architect insist this only applies to private balconies, specific to the dwelling unit. ICC technical support pointed out the text "of dwelling units and sleeping units" makes it sound dwelling unit specific, but by the end of the phone call indicated uncertainty and to look into NFPA13R. I did and 2016-NFPA13R Section 6.6.5.1 is nearly identical to 903.3.1.2.1 requiring sprinklers at Type VB roofed-balconies, decks, patios, as the only exception to 6.6.5 where NPFA13R specifies sprinklers not being required at "porches, balconies, corridors, carports, porte cocheres, and stairs that are open and attached." The annex for 6.6.5 provides an image of a wraparound corridor that appears to fit the bill of an egress balcony. Since the apts. don't have private balconies for the college student's bbq grill, I was excited to find reason for the egress balcony to be sprinklered, but now unclear, if that's enforceable. Thanks for any thoughts.