R-2 Existing Alarm
dmeyer
IL
We have an existing R-2 Occupancy that was built in 1960 and has current non functioning alarm system. The alarm is required under section 1103. The current nonfunctioning alarm panel, notification devices, and manual alarms will all be replaced with no other additions.
My question is the old system appears to be local alarm only, would the new installation require monitoring?
Thank you
Was there a code in effect in 1960? If so, what did that code require?
The 1960 code in effect is irrelevant, the IFC 1103 is a retroactive code section
SECTION 1103
FIRE SAFETY REQUIREMENTS
FOR EXISTING BUILDINGS
1103.1 Required construction.
Existing buildings shall comply with not less than the minimum provisions specified in Table 1103.1 and as further enumerated in Sections 1103.2 through 1103.10.
1103.7.6 Group R-2.
A manual fire alarm system that activates the occupant notification system in accordance with Section 907.5 shall be installed in existing Group R-2 occupancies more than three stories in height or with more than 16 dwelling or sleeping units.
1. Where each living unit is separated from other contiguous living units by fire barriers having a fire-resistance rating of not less than 3/4 hour, and where each living unit has either its own independent exit or its own independent stairway or ramp discharging at grade.
2. A separate fire alarm system is not required in buildings that are equipped throughout with an approved supervised automatic sprinkler system installed in accordance with Section 903.3.1.1 or 903.3.1.2 and having a local alarm to notify all occupants.
3. A fire alarm system is not required in buildings that do not have interior corridors serving dwelling units and are protected by an approved automatic sprinkler system installed in accordance with Section 903.3.1.1 or 903.3.1.2, provided that dwelling units either have a means of egress door opening directly to an exterior exit access that leads directly to the exits or are served by open-ended corridors designed in accordance with Section 1027.6, Exception 3.
4. A fire alarm system is not required in buildings that do not have interior corridors serving dwelling units, do not exceed three stories in height and comply with both of the following:
4.1. Each dwelling unit is separated from other contiguous dwelling units by fire barriers having a fire-resistance rating of not less than 3/4 hour.
4.2. Each dwelling unit is provided with hard-wired, interconnected smoke alarms as required for new construction in Section 907.2.10.
1103.8 Single- and multiple-station smoke alarms.
Single-and multiple-station smoke alarms shall be installed in existing Group I-1 and R occupancies in accordance with Sections 1103.8.1 through 1103.8.3.
1103.8.1 Where required.
Existing Group I-1 and R occupancies shall be provided with single-station smoke alarms in accordance with Section 907.2.10 Interconnection and power sources shall be in accordance with Sections 1103.8.2 and 1103.8.3, respectively.
1. Where the code that was in effect at the time of construction required smoke alarms and smoke alarms complying with those requirements are already provided.
2. Where smoke alarms have been installed in occupancies and dwellings that were not required to have them at the time of construction, additional smoke alarms shall not be required provided that the existing smoke alarms comply with requirements that were in effect at the time of installation.
3. Where smoke detectors connected to a fire alarm system have been installed as a substitute for smoke alarms.
1103.8.2 Interconnection.
Where more than one smoke alarm is required to be installed within an individual dwelling or sleeping unit, the smoke alarms shall be interconnected in such a manner that the activation of one alarm will activate all of the alarms in the individual unit. Physical interconnection of smoke alarms shall not be required where listed wireless alarms are installed and all alarms sound upon activation of one alarm. The alarm shall be clearly audible in all bedrooms over background noise levels with all intervening doors closed.
1. Interconnection is not required in buildings that are not undergoing alterations, repairs or construction of any kind.
2. Smoke alarms in existing areas are not required to be interconnected where alterations or repairs do not result in the removal of interior wall or ceiling finishes exposing the structure, unless there is an attic, crawl space or basement available that could provide access for interconnection without the removal of interior finishes.