• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

R-3 and attic access through garage ceiling

codeworks

Gold Member
Joined
Jun 12, 2011
Messages
579
Location
South Texas
how are you all addressing R-3 with attached garages with attic access through the garage ceiling? a large number of the "custom home builders " here put the attic access in the garage , which effectively kills the separation (1/4" plywood on drop down stairs. ) it has been "practice" if you will, that intumescent paint on this (eeeek!) has "been accepted". i don't like it, however, i'm looking for advise and other opinions. heavy handed ness " move the access to the inside of the home" doesn't go over well, any ideas? thanks. i'm thinking 1/2 drywall on stair "drop door" with a good seal to minimize smoke/air movement
 
We ask them to provide a listed rated attic access. There are companies that make 1 hr. rated access stairs. What we do not do is allow them to hang 5/8's type x on the cheap stair, because the added weight will cause it to sag and gap away from the ceiling. In most cases they drop the idea of having access from the garage.
 
screw some hinges to a piece of 5/8 plywood with 5/8 sheetrock attached to it and screw it above the stairway. do you allow 1/2" drywall on the garage ceiling when the attic space communicates freely with the living space attic?
 
i agree , 5/8 x is better, , we pretty much do "minimum code requirements" not many amendments, however, we're headed into a new code cycle, so maybe we can get some "tighter" stuff in (all depends on city council, builders board of appeals, ) we'll see
 
gbhammer said:
We amended the IRC to 5/8" type x for all garage separation, so no 1/2".
I'm amazed that you are more concerned about fires in garages than in assembly occupancies such as churches and educational occupancies such as daycares. One hour attic access in a house, seriously?
 
I just enforce what they give me. I don't make code or its amendments. It may be that upon occasion I push for one interpretation or the other, but it is ultimately left up to whomever the appointed CO happens to be. Then the code gets to go in front of a 6 person appointed board where they make their changes. If I interpret something that is disliked they can appeal and it is back in front of another 6 person appointed board.

Believe it or not I only want to do it right not spin my will upon the people.:beatdhrs
 
it's not that "im more concerned with fires in houses that assembly occupancies" we don't have any assembly occupancy's going up out here. i just started recently doing plan review here, which get re-reviewed by the assistant BO, and i'm trying to do the best i can. most (95%) of our construction is residential, we are in the country , not the city. if i had questions about other occupancies, i'd ask them.
 
codeworks he is just ornery, and likes to give us plan reviewers on the ropes. He knows so much it gets in the way of what the rest of us know.
 
i did some research when i was a plans reviewer in vermont, (1987) where , at the time, there were i believe 3 small jurisdictions doing any kind of residential inspection program at all. more people die in residential occupancies, than in fires that occur in public buildings. the reason is, most of our public buildings are occupied during the day, when people are awake and aware. with residential fires (this includes apartments, hotels, motels) there are way more vairables. you may be real careful, your neighbor may be smoking in bed and drinking a half gallon of whiskey, could lead to fire, kids play with matches, votive candles ( i hate those things, the wax burns down, glass breaks, hot wax drips off somewhere, flames follow wax) lots of variables. however, with residential fires, especially at night, people are sleepy, disoriented, not sure if they smell smoke or are dreaming, why is the dog barking, or the cat acting crazy, while all this plays out in the sleepy dreaming disorientad mind , flashover can occur in another room, now there's trouble . i could give a r@@s *SS if somebody jumps my concern. i've got big shoulders, i can take it and stand up to it.
 
So what's the big deal about residential garages? It's the cars. Cars burn like match heads, fast and furious. There was a smash-up and I saw smoke coming from under a car hood by the side of the freeway. I took me about 60 seconds to pull over, back up and deploy extinguishers. I was too late as the flames were 20' tall by then.

Here's a tip if you have an engine fire. Raise the hood just enough to get the extinguisher nozzle under the hood and pull the trigger. If you raise the hood all the way, the rush of air can make the fire grow real big, real fast. Then you're running down the street, on fire. I hate when that happens.

Heres another tip: One extinguisher is never enough.

The IRC watered down the requirements. I will allow as big a hole as you want. All that is required is an assembly that's listed for the purpose. For guidance one can consult the Mechanical Code which provides details for an access to a furnace through a bedroom. Ya I know, there is no reference to the Mechanical code in the Building code but it works to control the spread of smoke and fire. Don't forget about self closing and self latching, which kills the drop-down stair.

The first time a read the IRC requirement for only 1/2" drywall on the wall between a dwelling and an attached garage I thought "Shirley, I'm the only one that knows this." So far that's been the case. Not one contractor or civilian has challenged 5/8" type X. If anyone does challenge me, I'm going to tell them that that's a "back East" code and we don't do that here.
 
Last edited by a moderator:
Architect1281 said:
Why would it be any different than a door from the garage to the house.there are commercially available access doors that fill the bill
And boy oh boy do they fill a bill. The access can cost more than the entire ceiling.
 
If attaching the appropriate ceiling cover over the door does not cause it to "sag" so that it does in fact seal, just as any other drop in access cover, there is no reason not to accept it. JMHO
 
The attic isn't living space, the type x doesn't need to be on the garage ceiling at all. The type x goes on the garage/house wall all the way to the roof and that's the end of it.
 
ICE said:
Here's a tip if you have an engine fire. Raise the hood just enough to get the extinguisher nozzle under the hood and pull the trigger. If you raise the hood all the way, the rush of air can make the fire grow real big, real fast. Then you're running down the street, on fire. I hate when that happens. Heres another tip: One extinguisher is never enough.

or go into the bed of your truck, open your igloo cooler, pull out a can of beer and shake it up. next open the hood enough for a can of beer to fit, pop the top, toss it into the engine compartment and close the hood. instant fire extinguisher!
 
GBrackins said:
ICE said:
Here's a tip if you have an engine fire. Raise the hood just enough to get the extinguisher nozzle under the hood and pull the trigger. If you raise the hood all the way, the rush of air can make the fire grow real big, real fast. Then you're running down the street, on fire. I hate when that happens. Heres another tip: One extinguisher is never enough.

or go into the bed of your truck, open your igloo cooler, pull out a can of beer and shake it up. next open the hood enough for a can of beer to fit, pop the top, toss it into the engine compartment and close the hood. instant fire extinguisher!
So you pull over every time you need a beer?:devil
 
Last edited by a moderator:
Greetings all,

Yea we have had 2 house fires in the last year or so that started in the garage, spread into the attic thereby pretty much destroying everything. Interestingly, at both fires there were folks at home and awake and yet still damage was significant. Older homes though. I don't think either had a solid 20 minute separation.

BS
 
Top