I am doing a plan review for a group R-3 Building. Using codes 2009IBC/ANSI A117.1-2003
6 bedroom, 2 story building being used for employees to live at a sumer camp. An small office and a kitchen on 1st. floor. No elevator needed for 2nd floor acording to 1107.7.1.2.
The plans show 2 bedrooms on the 1st floor. One bedroom has an accessible bathroom. There is also a bathroom in the hall that is not accessible. 4 bedrooms on the 2nd floor. One bedroom has an accessible bathroom. Also a bathroom in the hall that is not accessible.
IBC 1107,6.3 says in R-3 all units must be "type B" units. 1107.7.1.1, 1107.7.1.2 1 and 1107.7.2 says only the 1st floor needs to have type B units.
It looks like the bathroom in the 1st floor hall needs to be fully accessible because of the office. i'm not sure about the bathroom in the hall of the 2nd floor. 1107.3 says that the bathroom needs to be accessable if it is available for use by residents and serving accessible, type A or type B units.
The Units on the 2nd floor do not need to be accessible, A, or B. But the bathroom on the 2nd floor hall could be used by the B units on the 1st floor. There is no accessible route to the 2nd floor.
Does the 2nd floor hall bathroom need to be accessible?
6 bedroom, 2 story building being used for employees to live at a sumer camp. An small office and a kitchen on 1st. floor. No elevator needed for 2nd floor acording to 1107.7.1.2.
The plans show 2 bedrooms on the 1st floor. One bedroom has an accessible bathroom. There is also a bathroom in the hall that is not accessible. 4 bedrooms on the 2nd floor. One bedroom has an accessible bathroom. Also a bathroom in the hall that is not accessible.
IBC 1107,6.3 says in R-3 all units must be "type B" units. 1107.7.1.1, 1107.7.1.2 1 and 1107.7.2 says only the 1st floor needs to have type B units.
It looks like the bathroom in the 1st floor hall needs to be fully accessible because of the office. i'm not sure about the bathroom in the hall of the 2nd floor. 1107.3 says that the bathroom needs to be accessable if it is available for use by residents and serving accessible, type A or type B units.
The Units on the 2nd floor do not need to be accessible, A, or B. But the bathroom on the 2nd floor hall could be used by the B units on the 1st floor. There is no accessible route to the 2nd floor.
Does the 2nd floor hall bathroom need to be accessible?