For some reason I've found myself confused about the requirements for draftstopping in R2, 2018 IBC. Hoping someone can help me clarify the intent.
The building in question is VB, R2 (8 units), 2 story, 36ft in height, 24" open web floor trusses, pitched roof trusses.
Fully sprinkled, NFPA 13, including the attic, but not including the floor/ceiling cavity.
Floor/ceiling horiz assembly = 1/2 hr (711.2.4, exception) (dividing dwelling units)
Fire Partitions dividing dwelling units = 1/2 hr (per 420.2, 1/2 hr per 708.3, exception 2)
Fire Partitions at Corridors = 1/2 hr (fire partitions per 420.2, 1/2 hr per 708.3, exception 1)
Question is if draftstops are required in the attic and/or floor/ceiling space if the attic is sprinkled, but floor/ceiling is not?
For the attic (which is sprinkled), 708.4.2=
Exception 1 = no draftstopping required with sprinklers
Exception 4 = draftstops required because it is R2/etc
718.4 requires draftstops as required in 708.4.2, but an exception for being sprinkled.
Conclusion: sprinkled attic does not need draftstops.
For the floor/ceiling (not sprinkled), 708.4.2=
Exception 2 = draftstopping only required above one of the corridor walls
718.3 says draftstopping required per 708.4.2 - so above corridor walls
Conclusion: draftstopping required above corridor walls
(note if this was not R2, the floor/ceiling would be required to be subdivided into 1,000sf max areas)
708.4.2 Fireblocks and draftstops in combustible construction.
In combustible construction where fire partitions do not extend to the underside of the floor or roof sheathing, deck or slab above, the space above and along the line of the fire partition shall be provided with one of the following:
718.3 Draftstopping in floors. Draftstopping shall be installed to subdivide floor/ceiling assemblies where required by Section 708.4.2. In other than Group R occupancies, draftstopping shall be installed to subdivide combustible floor/ceiling assemblies so that the horizontal floor areas do not exceed 1,000 square feet.
Exception: Buildings equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1.
718.4 Draftstopping in attics. Draftstopping shall be installed to subdivide attic spaces where required by Section 708.4.2. In other than Group R, draftstopping shall be installed to subdivide combustible attic spaces and combustible concealed roof spaces such that any horizontal area does not exceed 3,000 square feet. Ventilation of concealed roof spaces shall be maintained in accordance with 1202.2.1.
Exception: Buildings equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1.
Sorry for the long post...hopefully I included enough info for feedback.
Thanks in advance!
The building in question is VB, R2 (8 units), 2 story, 36ft in height, 24" open web floor trusses, pitched roof trusses.
Fully sprinkled, NFPA 13, including the attic, but not including the floor/ceiling cavity.
Floor/ceiling horiz assembly = 1/2 hr (711.2.4, exception) (dividing dwelling units)
Fire Partitions dividing dwelling units = 1/2 hr (per 420.2, 1/2 hr per 708.3, exception 2)
Fire Partitions at Corridors = 1/2 hr (fire partitions per 420.2, 1/2 hr per 708.3, exception 1)
Question is if draftstops are required in the attic and/or floor/ceiling space if the attic is sprinkled, but floor/ceiling is not?
For the attic (which is sprinkled), 708.4.2=
Exception 1 = no draftstopping required with sprinklers
Exception 4 = draftstops required because it is R2/etc
718.4 requires draftstops as required in 708.4.2, but an exception for being sprinkled.
Conclusion: sprinkled attic does not need draftstops.
For the floor/ceiling (not sprinkled), 708.4.2=
Exception 2 = draftstopping only required above one of the corridor walls
718.3 says draftstopping required per 708.4.2 - so above corridor walls
Conclusion: draftstopping required above corridor walls
(note if this was not R2, the floor/ceiling would be required to be subdivided into 1,000sf max areas)
708.4.2 Fireblocks and draftstops in combustible construction.
In combustible construction where fire partitions do not extend to the underside of the floor or roof sheathing, deck or slab above, the space above and along the line of the fire partition shall be provided with one of the following:
- Fireblocking up to the underside of the floor or roof sheathing, deck or slab above using materials complying iwth Section 718.2.1.
- Draftstopping up to the underside of the floor or roof sheathing, deck or slab above using materials complying with section 718.3.1 for floors or Section 718.4.1 for attics.
- Buildings equipped with an automatic sprinkler system installed throughout in accordance with Section 903.3.1.1, or in accordance with Section 903.3.1.2 provided that protection is provided in the space between the top of the fire partition and underside of the floor or roof sheathing, deck or slab above as required for systems complying with Section 903.3.1.1.
- Where corridor walls provide a sleeping unit or dwelling unit separation, draftstopping shall only be required above one of the corridor walls.
- In Group R2 occupancies with fewer than four dwelling units, fireblocking and draftstopping shall shall not be required.
- In Group R2 occupancies up to and including four stories in height in buildings not exceeding 60 ft in height above grade plane, the attic space shall be subdivided by draftstops into areas not exceeding 3,000 square feet or above every two dwelling units, whichever is smaller.
- In Group R3 occupancies with fewer than three dwelling units, fireblocking and draftstopping shall not be required in floor assemblies.
718.3 Draftstopping in floors. Draftstopping shall be installed to subdivide floor/ceiling assemblies where required by Section 708.4.2. In other than Group R occupancies, draftstopping shall be installed to subdivide combustible floor/ceiling assemblies so that the horizontal floor areas do not exceed 1,000 square feet.
Exception: Buildings equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1.
718.4 Draftstopping in attics. Draftstopping shall be installed to subdivide attic spaces where required by Section 708.4.2. In other than Group R, draftstopping shall be installed to subdivide combustible attic spaces and combustible concealed roof spaces such that any horizontal area does not exceed 3,000 square feet. Ventilation of concealed roof spaces shall be maintained in accordance with 1202.2.1.
Exception: Buildings equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1.
Sorry for the long post...hopefully I included enough info for feedback.
Thanks in advance!