• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

R317.3.3 How do you verfy compliance in the field?

mtlogcabin

SAWHORSE
Joined
Oct 17, 2009
Messages
9,556
Location
Big Sky Country
What is a simple way to verify in the field the proper fasteners are used? Our big concern is the staples used in the fire-retardant roof sheathing required on townhouses. When we get there for the inspections the jobsites are swept clean so no empty boxes to verify what was used?

R317.3.3 Fasteners for fire-retardant-treated wood used in exterior applications or wet or damp locations.

Fasteners for fire-retardant-treated wood used in exterior applications or wet or damp locations shall be of hot-dipped zinc-coated galvanized steel, stainless steel, silicon bronze or copper. Fasteners other than nails and timber rivets shall be permitted to be of mechanically deposited zinc-coated steel with coating weights in accordance with ASTM B 695, Class 55 minimum.
 
You might want to have them pull one.

Would not be surprised if the contractor had an empty box of the correct fastener specifically to show the inspector. This may different from the box the other fasteners came out of.
 