R609 Exterior Windows & Doors
Reads like this in Florida. (partial)
SECTIONR609
EXTERIOR WINDOWS AND DOORS​
R609.1General.​
This section prescribes performance and construction requirements for exterior windows and doors installed in walls. Windows and doors shall be installed and flashed in accordance with the fenestration manufacturer’s written instructions. Window and door openings shall be flashed in accordance with Section R703.4. Written installation instructions shall be provided by the fenestration manufacturer for each window or door.
R609.2Performance.​
Exterior windows and doors shall be designed to resist the design wind loads specified in Table R301.2(2) adjusted for height and exposure in accordance with Table R301.2(3) or determined in accordance with ASCE 7 using the allowable stress design load combinations of ASCE 7. Design wind loads for exterior glazing not part of a labeled assembly shall be permitted to be determined in accordance with Chapter 24 of the Florida Building Code, Building.
R609.2.1Custom doors.​
Custom (one-of-a-kind) exterior door assemblies shall be tested by an approved testing laboratory or be designed and engineered in accordance with accepted engineering practices by a Florida registered design professional. Signed and sealed copies of the rational analysis and calculations shall be provided to the building official upon permit application.
R609.3Testing and labeling.​
Exterior windows and sliding doors shall be tested by an approved independent laboratory, and bear a label identifying manufacturer, performance characteristics and approved inspection agency to indicate compliance with AAMA/WDMA/CSA 101/I.S.2/A440 or TAS 202 (HVHZ shall comply with TAS 202 and ASTM E1300). Exterior side-hinged doors shall be tested and labeled as conforming to AAMA/WDMA/CSA 101/I.S.2/A440 or ANSI/WMA 100, or comply with Section R609.5. Exterior windows and doors shall be labeled with a permanent label, marking, or etching providing traceability to the manufacturer and product. The following shall also be required either n a permanent label or on a temporary supplemental label applied by the manufacturer: information identifying the manufacturer, the product model/series number, positive and negative design pressure rating, product maximum size tested, impact-resistance rating if applicable, Florida product approval number or Miami-Dade product approval number applicable test standard(s), and approved product certification agency, testing laboratory, evaluation entity or Miami-Dade product approval.
The labels are limited to one design pressure rating per reference standard. The temporary supplemental label shall remain on the window or door until final approval by the building official.