1:150 rule does not require a 50:50 balance upper vs lower. 1:300 requires approx 50:50 balance.
So a 3000sf attic requires 10sf of venting IF 5 to 6sf are lower, and 4 to 5sf are upper (min 40% max 50% in upper third). So 8sf upper and 2sf lower breaks this rule. That much is clear. Also 2sf upper and 8sf lower breaks this rule. What about 4sf upper and 12sf lower?
In this example we break the min 40% requirement for the 1:300 rule, but use of the words "...not less than 40% or more than 50% of the REQUIRED ventilating area must be in the top 1/3..." muddies the water as follows:
using the 1:300 rule, 10 square feet of ventilators are REQUIRED. So if i exceed the minimum by providing 16 square feet of venting, but do not reach an amount that satisfies the 1:150 rule, do i need 40% to 50% of the "REQUIRED" 10 square feet to be in the upper third (which would make my "4sf upper/12sf lower" example perfectly acceptable), or do I need 40% to 50% of WHAT I ACTUALLY PROVIDE to be in the upper third (meaning i would need min 6.4sf upper, and therefore my 4:12 example is a violation)?
My suspicion is that the near 50/50 balance is required for speed of air movement (i.e. air flow relies on the "stack effect" at this ratio). At low venting ratios air speed is more critical since it is the only force present that can move water vapor out of the attic (I'm speculating here), so balance has to be maintained at all ratios below 1:150 to preserve the stack effect. Air moves upward and out the vent as it warms against yhe roof sheathing, pulling cold air in at the lowest opening to replace it. The stack effect is foiled if upper and lower are not in balance (same reason barely opening the door of a wood stove causes rapid air movement into the fire, but fully opening it slows it down. More isn't always more).
At 1:150, the stack effect is no longer required because there is enough vent area to allow the combined pressures of "diffusion" and the "ideal gas law" to move water vapor out of the attic and into the open air outside.
Thoughts?
So a 3000sf attic requires 10sf of venting IF 5 to 6sf are lower, and 4 to 5sf are upper (min 40% max 50% in upper third). So 8sf upper and 2sf lower breaks this rule. That much is clear. Also 2sf upper and 8sf lower breaks this rule. What about 4sf upper and 12sf lower?
In this example we break the min 40% requirement for the 1:300 rule, but use of the words "...not less than 40% or more than 50% of the REQUIRED ventilating area must be in the top 1/3..." muddies the water as follows:
using the 1:300 rule, 10 square feet of ventilators are REQUIRED. So if i exceed the minimum by providing 16 square feet of venting, but do not reach an amount that satisfies the 1:150 rule, do i need 40% to 50% of the "REQUIRED" 10 square feet to be in the upper third (which would make my "4sf upper/12sf lower" example perfectly acceptable), or do I need 40% to 50% of WHAT I ACTUALLY PROVIDE to be in the upper third (meaning i would need min 6.4sf upper, and therefore my 4:12 example is a violation)?
My suspicion is that the near 50/50 balance is required for speed of air movement (i.e. air flow relies on the "stack effect" at this ratio). At low venting ratios air speed is more critical since it is the only force present that can move water vapor out of the attic (I'm speculating here), so balance has to be maintained at all ratios below 1:150 to preserve the stack effect. Air moves upward and out the vent as it warms against yhe roof sheathing, pulling cold air in at the lowest opening to replace it. The stack effect is foiled if upper and lower are not in balance (same reason barely opening the door of a wood stove causes rapid air movement into the fire, but fully opening it slows it down. More isn't always more).
At 1:150, the stack effect is no longer required because there is enough vent area to allow the combined pressures of "diffusion" and the "ideal gas law" to move water vapor out of the attic and into the open air outside.
Thoughts?