I wanted to reach out and see how other departments have been addressing this issue, as we have had some confusion from contractors and architects. With families living in these new homes it is important that we get this stuff right, to avoid mold/moisture issues or unnecessary financial loss. So here goes...
It is a common trend in local new construction to stucco the soffits without vents and spray foam insulation in the attic below the roof sheathing and above the soffits. These unvented attics are allowed per R806. The problem arises when a knee wall is built and sprayed with insulation separating the garage or outdoor living attics from the rest of the attic space.
By spraying these knee walls we are moving the building thermal envelope to the knee wall and isolating the garage or lanai, which make them no longer conditioned spaces and ineligible for being unvented (See R806.5(1) below).
[RE] BUILDING THERMAL ENVELOPE. The basement walls, exterior walls, floor, roof and any other building element that enclose conditioned spaces. (Also see Section R202 of the Florida Building Code, Energy Conservation.)
[RE] CONDITIONED SPACE. An area, room or space that is enclosed within the building thermal envelope and that is directly heated or cooled or that is indirectly heated or cooled. Spaces are indirectly heated or cooled where they communicate thru openings with conditioned spaces, where they are separated from conditioned spaces by uninsulated walls, floors or ceilings or where they contain uninsulated ducts, piping or other sources of heating or cooling.
Thanks for your time and consideration. I look forward to seeing your thoughts on the matter, and seeing how others are crossing this bridge.
It is a common trend in local new construction to stucco the soffits without vents and spray foam insulation in the attic below the roof sheathing and above the soffits. These unvented attics are allowed per R806. The problem arises when a knee wall is built and sprayed with insulation separating the garage or outdoor living attics from the rest of the attic space.
By spraying these knee walls we are moving the building thermal envelope to the knee wall and isolating the garage or lanai, which make them no longer conditioned spaces and ineligible for being unvented (See R806.5(1) below).
Some contractors have sprayed the bottom chords of the garage/lanai and removed the knee wall, bringing them back into the thermal envelope.
This change may affect the energy calculations and require a rated attic access to maintain garage separation
Others have gone back after the fact and added soffit or ridge vents to these garage/lanai attic spaces and kept the sprayed knee wall.
I have been told by a few insulation contractors that open cell foam should not be used in vented, unconditioned attic space because it will collect moisture.
We have also had architects revise the plan and add a mini-split to the garage, conditioning the garage and in so doing, indirectly conditioning the attic above it as well.
It's not exactly cost effective to condition the garage in Florida, as it will all be gone the second the garage door opens, and there may be loss of efficiency if there are hydrostatic vents
[RE] BUILDING THERMAL ENVELOPE. The basement walls, exterior walls, floor, roof and any other building element that enclose conditioned spaces. (Also see Section R202 of the Florida Building Code, Energy Conservation.)
[RE] CONDITIONED SPACE. An area, room or space that is enclosed within the building thermal envelope and that is directly heated or cooled or that is indirectly heated or cooled. Spaces are indirectly heated or cooled where they communicate thru openings with conditioned spaces, where they are separated from conditioned spaces by uninsulated walls, floors or ceilings or where they contain uninsulated ducts, piping or other sources of heating or cooling.
SECTION R806 Roof Ventilation
R806.1
Enclosed attics and enclosed rafter spaces formed where ceilings are applied directly to the underside of roof rafters shall have cross ventilation for each separate space by ventilating openings protected against the entrance of rain or snow. Ventilation openings shall have a least dimension of 1/16 inch (1.6 mm) minimum and 1/4 inch (6.4 mm) maximum. Ventilation openings having a least dimension larger than 1/4 inch (6.4 mm) shall be provided with corrosion-resistant wire cloth screening, hardware cloth, perforated vinyl or similar material with openings having a least dimension of 1/16 inch (1.6 mm) minimum and 1/4 inch (6.4 mm) maximum. Openings in roof framing members shall conform to the requirements of Section R802.7. Required ventilation openings shall open directly to the outside air and shall be protected to prevent the entry of birds, rodents, snakes and other similar creatures.
R806.2
The minimum net free ventilating area shall be 1/150 of the area of the vented space.
Exception: The minimum net free ventilation area shall be 1/300 of the vented space, provided that not less than 40 percent and not more than 50 percent of the required ventilating area is provided by ventilators located in the upper portion of the attic or rafter space. Upper ventilators shall be located not more than 3 feet (914 mm) below the ridge or highest point of the space, measured vertically. The balance of the required ventilation provided shall be located in the bottom one-third of the attic space. Where the location of wall or roof framing members conflicts with the installation of upper ventilators, installation more than 3 feet (914 mm) below the ridge or highest point of the space shall be permitted.
R806.3
Where eave or cornice vents are installed, blocking, bridging and insulation shall not block the free flow of air. Not less than a 1-inch (25 mm) space shall be provided between the insulation and the roof sheathing and at the location of the vent.
R806.4
Ventilators shall be installed in accordance with manufacturer’s instructions. Installation of ventilators in roof systems shall be in accordance with the requirements of Section R903. Installation of ventilators in wall systems shall be in accordance with the requirements of Section R703.1.
R806.5
Unvented attics and unvented enclosed roof framing assemblies created by ceilings that are applied directly to the underside of the roof framing members and structural roof sheathing applied directly to the top of the roof framing members/rafters, shall be permitted where all the following conditions are met:
1.The unvented attic space is completely within the building thermal envelope.
2.No interior Class I vapor retarders are installed on the ceiling side (attic floor) of the unvented attic assembly or on the ceiling side of the unvented enclosed roof framing assembly.
3.Where wood shingles or shakes are used, a minimum 1/4-inch (6.4 mm) vented airspace separates the shingles or shakes and the roofing underlayment above the structural sheathing.
4.In Climate Zones 5, 6, 7 and 8, any air-impermeable insulation shall be a Class II vapor retarder, or shall have a Class II vapor retarder coating or covering in direct contact with the underside of the insulation.
5.Insulation shall comply with Item 5.3 and Item 5.1. As an alternative, where air-permeable insulation is located on top of the attic floor or on top of the attic ceiling, insulation shall comply with Item 5.3 and Item 5.2.
5.1.Item 5.1.1, 5.1.2, 5.1.3 or 5.1.4 shall be met, depending on the air permeability of the insulation directly under the structural roof sheathing.
5.1.1.Where only air-impermeable insulation is provided, it shall be applied in direct contact with the underside of the structural roof sheathing.
5.1.2.Where air-permeable insulation is provided inside the building thermal envelope, it shall be installed in accordance with Section 5.1.1. In addition to the air-permeable insulation installed directly below the structural sheathing, rigid board or sheet insulation shall be installed directly above the structural roof sheathing in accordance with the R-values in Table R806.5 for condensation control.5.1.3.Where both air-impermeable and air-permeable insulation are provided, the air-impermeable insulation shall be applied in direct contact with the underside of the structural roof sheathing in accordance with Item 5.1.1 and shall be in accordance with the R-values in Table R806.5 for condensation control. The air-permeable insulation shall be installed directly under the air-impermeable insulation.5.1.4.Alternatively, sufficient rigid board or sheet insulation shall be installed directly above the structural roof sheathing to maintain the monthly average temperature of the underside of the structural roof sheathing above 45°F (7°C). For calculation purposes, an interior air temperature of 68°F (20°C) is assumed and the exterior air temperature is assumed to be the monthly average outside air temperature of the three coldest months.5.2.In Climate Zones 1, 2 and 3, air-permeable insulation installed in unvented attics on the top of the attic floor or on top of the ceiling shall meet the following requirements:
- 5.2.1.An approved vapor diffusion port shall be installed not more than 12 inches (305 mm) from the highest point of the roof, measured vertically from the highest point of the roof to the lower edge of the port.
- 5.2.2.The port area shall be greater than or equal to 1:600 of the ceiling area. Where there are multiple ports in the attic, the sum of the port areas shall be greater than or equal to the area requirement.
- 5.2.3.The vapor-permeable membrane in the vapor diffusion port shall have a vapor permeance rating of greater than or equal to 20 perms when tested in accordance with Procedure A of ASTM E96.
- 5.2.4.The vapor diffusion port shall serve as an air barrier between the attic and the exterior of the building.
- 5.2.5.The vapor diffusion port shall protect the attic against the entrance of rain and snow.
- 5.3.Where preformed insulation board is used as the air-impermeable insulation layer, it shall be sealed at the perimeter of each individual sheet interior surface to form a continuous layer.
Thanks for your time and consideration. I look forward to seeing your thoughts on the matter, and seeing how others are crossing this bridge.