The ceilings joists in the picture are parallel to the rafters, so it would be the next line in the table, which directs you to R802.5.2. Section R802.5.2.1 tells you the lap connections have to be the equivalent of the ceiling joist to rafter connection specified in Table R802.5.2(1).So this is what they are trying to rercreate:
I recommend a Simpson VB-7...but it is way overkill, but you can point to it in the book, so it is easy.......You are looking at controlling about 400# if you are using the prescriptive nail connection...
View attachment 11170
Referring to the ledger nails. I had it in my head that they should be closer, but the current codes don't give a dimension, and the code I thought they exceeded calls it 4" o/c, so these are probably fine. Ledger framing provides a much better finish, produces less squeaks, and is cheaper and quicker. JMHO.I don’t see the problem. Looks like 3 toe nails from the joist, part way into the beam web … we always do it that way …
You mean this?Referring to the ledger nails. I had it in my head that they should be closer, but the current codes don't give a dimension, and the code I thought they exceeded calls it 4" o/c, so these are probably fine. Ledger framing provides a much better finish, produces less squeaks, and is cheaper and quicker. JMHO.
No collar ties, but if there were, they still don't count for rafter thrust.Jar, are there any collar or rafter ties above the CJ/Beam connections to prevent spread?
Yes. Back in the day in another state with a state code, they prescribed it in this table and I guess I mis-remembered it as "within 3" of the joist, so one nail under and 2 or 3 within 3" of the joist. But, I went back and can only find that it says 4" o/c. It may have come from an earlier edition, or it may be that I have been wrong all along, and current code has no distance prescription anyway with "At each joist".
Relative to tension force from inside ends of attic floor joists, at main beam (girder).......... that resist outward thrust force from low ends of rafters;
Angled nails ("toenails").........installed to connect inside end of attic floor joists to side face of main beam........are not resisting force from attic floor joists as shear force in "normal" way considered for NDS provisions governing design shear capacity for toenails.......which is for downward-acting force due to vertical load on joists. Such nails resist tension force from floor joists mostly in withdrawal (from main beam).......and are susceptible to weakening over time with cycles of snow load on roof. For relatively small outward thrust force........such connections can work...........however, for larger houses and lower-slope roof, such connections are not adequate.
If top of beam is flush with top of floor joists, then most effective method for resisting outward thrust force from low ends of rafters is to install plywood floor sheathing......even if only 4-feet wide.........securely nailed to attic floor joists on each side of beam.
Other method that should be considered ........if main beam is available...........is to design beam to support ridge member (of roof) along with attic floor load.
Snow load and floor live load can be reduced when both design loads are combined for same load case.
Simpson connector shown in previous post surely can work...........though not really required for every joist if plywood can be installed on floor joists on each side of beam. Install strip of plywood (4-feet wide is best) on each side of beam, securely nailed to joists with 8d nails at 6-inches or less. Narrow open-strip can be provided adjacent to each side of beam to provide clear access for installation of connectors (to joist and beam)..........which could likely be spaced at every third joist or even more, depending on allowable tension capacity and required thrust force. Plywood will essentially span between connectors as deep horizontal beam.......or "diaphragm".
Other connectors can be used with same approach.
Responding to issues in thread...........not asking question.I didn't understand anything you wrote. Something abut attic floor joists? How did you get from that to ridge beams?
Please explain you question better.