Thanks for all your responses. Here's what I'm writing the applicant:
Submit sufficient technical data to substantiate the proposed design and to prove that the exterior walls’ performance meets the intent of this code per Section 106.5.3 RCO.
Alterations shall conform to code requirements for new construction and not be made to an existing residential building which will cause the existing building to be in violation of any provisions of this code per Section 113.4 RCO.
Buildings and parts thereof shall safely support all loads including dead loads, live loads, and roof loads as prescribed by this code per Section 301.1 RCO.
List on the drawings the minimum live loads for the existing roof as indicated in Table 301.6 or the snow load as indicated in Table 301.2(1) based upon Figure 301.2(6), whichever is greater per Section 301.6 RCO.
The allowable deflection of the existing exterior walls under the live load listed in Sections 301.5 and 301.6 shall not exceed the values in Table 301.7 per Section 301.7 RCO.