Rang Hoods for residential cooking equpment

Moscow

Bronze Member
Joined
Nov 9, 2009
Messages
99
Location
Moscow Idaho
I have been disscussing with the BO about if rang hoods are requied over cooking equpment in residential homes. I beleive that the code dose not require them but if you do install them you have to follow the CFM table. My BO thinks they have to be installed when a rang is installed.

Just wondering how your area is enforcing this requirment and if you have a code section.

Thanks for you help

and you all have a wonderful weekend.
 
I don't know why they don't put it at the front of the section, but M1503.3 says "where they are equipped". So they aren't required. However Oregon has an amendment requiring them.

M1503.3 Kitchen exhaust rates. Where domestic kitchen

cooking appliances are equipped with ducted range hoods or

down-draft exhaust systems, the fans shall be sized in accordance

with Section M1507.3.
 
Agreed, not required, but if installed, follow manufacturer's specs or code, whichever is more restrictive.
 
Thanks for all the replies on this matter.

I will have to apologize for all the spelling errors in my post after reading it back it is horrible
 
High Desert said:
I don't know why they don't put it at the front of the section, but M1503.3 says "where they are equipped". So they aren't required. However Oregon has an amendment requiring them.M1503.3 Kitchen exhaust rates. Where domestic kitchen

cooking appliances are equipped with ducted range hoods or

down-draft exhaust systems, the fans shall be sized in accordance

with Section M1507.3.
i agree with others, not required
 
me too... me too...

(and don't install PVC vent pipe if you intend to vent to the outside).
 
McShan said:
PVC is only for dryer venting
Where did you get this information? PVC can be used for down draft range hood ducting when encased in cement. PVC can not be used for clothes dryer vent according to the current IRC residential building code.
 
Funny, as a private inspector of a new home for a buyer I found a downdraft exhaust whose duct went no further than the next bay in the base unit.
 
JohnPeitsmeyer said:
Where did you get this information? PVC can be used for down draft range hood ducting when encased in cement. PVC can not be used for clothes dryer vent according to the current IRC residential building code.
John take a look at IMC section 505 505.1 exception 2 through 2.5 schedule 40 PVC is allowed with exceptions.
 
Be carefull over high end ranges they often have more restrictive requiremnets. I had a wolfe range that would not allow a stainless steel hood and vent closer than 36" to the rang. It was originally only 30".
 