OK, so we are all aware of this:
I thought they were going to tighten this up when they added the 400cfm makeup air code.
Thoughts?
Then there is this:M1501.1 Outdoor discharge. The air removed by everymechanical exhaust system shall be discharged to the outdoors.
Air shall not be exhausted into an attic, soffit, ridge vent or
crawl space.
Exception: Whole-house ventilation-type attic fans that
discharge into the attic space of dwelling units having private
attics shall be permitted
The last exception essentially cancels out the requirement because just about every single recirculating hood is listed and labeled. A kitchen with an operable window meets the ventilation exception.RANGE HOODSM1503.1 General. Range hoods shall discharge to the outdoors
through a single-wall duct. The duct serving the hood
shall have a smooth interior surface, shall be air tight and shall
be equipped with a backdraft damper. Ducts serving range
hoods shall not terminate in an attic or crawl space or areas
inside the building.
Exception: Where installed in accordance with the manufacturer’s
installation instructions, and where mechanical or
natural ventilation is otherwise provided, listed and labeled
ductless range hoods shall not be required to discharge to
the outdoors.
I thought they were going to tighten this up when they added the 400cfm makeup air code.
Thoughts?