Hello Everyone,
Hope you guys can help me out on the building code.
I'm having a house built by a production builder and I asked why my Gas Cooktop has a recirculating range and not a vented one. Their answer was it isn't required in South Carolina. I've asked to pay for it to be vented and they refused. They've told me if you can show it is violating the code they will do it as right now the production builder sub contracts the HVAC and Kitchen Appliances to one supplier. So they just don't wait to pay for it if it's required.
I've been doing some digging for about two weeks and even reached out to the City's inspectors. They pointed me to the IRC 2015
Section M1503 Range Hoods
M1503.1 General
Range hoods shall discharge to the outdoors through a duct. The duct serving the hood shall have a smooth interior surface, shall be air tight, shall be equipped with a back-draft damper and shall be independent of all other exhaust systems. Ducts serving range hoods shall not terminate in an attic or crawl space or areas inside the building.
Exception: Where installed in accordance with the manufacturer's instructions, and where mechanical or natural ventilation is otherwise provided, listed and labeled ductless range hoods shall not be required to discharge to the outdoors.
They are considering a recirculating fan a mechanical ventilation... It's pushing the air back in the room... I find it kind of pointless, the carbon filters will catch some of the grease and bad smell but the Carbon Monoxide, Formaldehyde, and Moisture will just be recirculating in the room.
======> Question 1. Is a recirculating vent acceptable?
M1507.4 Local Exhaust Rates
Local exhaust systems shall be designed to have the capacity to exhaust the minimum air flow rate determined in accordance with Table M1507.4.
TABLE M1507.4
MINIMUM REQUIRED LOCAL EXHAUST RATES FOR ONE- AND TWO-FAMILY DWELLINGS
For SI: 1 cubic foot per minute = 0.0004719 m3/s.
======> Question 2. Does this mean it has to be exhausted to the outside?
Thank you in advance
Hope you guys can help me out on the building code.
I'm having a house built by a production builder and I asked why my Gas Cooktop has a recirculating range and not a vented one. Their answer was it isn't required in South Carolina. I've asked to pay for it to be vented and they refused. They've told me if you can show it is violating the code they will do it as right now the production builder sub contracts the HVAC and Kitchen Appliances to one supplier. So they just don't wait to pay for it if it's required.
I've been doing some digging for about two weeks and even reached out to the City's inspectors. They pointed me to the IRC 2015
Section M1503 Range Hoods
M1503.1 General
Range hoods shall discharge to the outdoors through a duct. The duct serving the hood shall have a smooth interior surface, shall be air tight, shall be equipped with a back-draft damper and shall be independent of all other exhaust systems. Ducts serving range hoods shall not terminate in an attic or crawl space or areas inside the building.
Exception: Where installed in accordance with the manufacturer's instructions, and where mechanical or natural ventilation is otherwise provided, listed and labeled ductless range hoods shall not be required to discharge to the outdoors.
They are considering a recirculating fan a mechanical ventilation... It's pushing the air back in the room... I find it kind of pointless, the carbon filters will catch some of the grease and bad smell but the Carbon Monoxide, Formaldehyde, and Moisture will just be recirculating in the room.
======> Question 1. Is a recirculating vent acceptable?
M1507.4 Local Exhaust Rates
Local exhaust systems shall be designed to have the capacity to exhaust the minimum air flow rate determined in accordance with Table M1507.4.
TABLE M1507.4
MINIMUM REQUIRED LOCAL EXHAUST RATES FOR ONE- AND TWO-FAMILY DWELLINGS
AREA TO BE EXHAUSTED | EXHAUST RATES |
Kitchens | 100 cfm intermittent or 25 cfm continuous |
Bathrooms-Toilet Rooms | Mechanical exhaust capacity of 50 cfm intermittent or 20 cfm continuous |
======> Question 2. Does this mean it has to be exhausted to the outside?
Thank you in advance