• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Range Hood tied into general exhaust.

JBI said:
The jpg in the OP says 'Office Building' at the bottom yet it is posted in the Residential Mechanical section. So I guess the OP needs to come back and clarify for us.

Perhaps he saw the first responses, realized the arrangement was not compliant and quietly sipped away?
It also said it was IBC compliant
 
cda said:
have not seen an inline before in a systemSo does the inline run 24 hours a day???
It depends, they can be tied into occupant sensors or timers. Either way this is not a very good design. Generally you don't want to mix exhaust air from kitchens and bathrooms. It's just poor building practice.
 
2012 IMC

507.2.3 Domestic cooking appliances used for commercial purposes.

Domestic cooking appliances utilized for commercial purposes shall be provided with Type I or Type II hoods as required for the type of appliances and processes in accordance with Sections 507.2, 507.2.1 and 507.2.2.

The domestic hood does not comply. Thee are NO exceptions to this sub-section.
 