NEC 250.140 – 2020 vs. 2023
The 2023 NEC reorganized and clarified Section 250.140, which governs how the frames of electric ranges, ovens, cooking units, and clothes dryers must be grounded. In the 2020 NEC, this section included an exception allowing the use of the grounded (neutral) conductor for bonding the frame on existing branch circuits without an equipment grounding conductor (EGC). That structure was replaced in 2023 with two subsections: (A) for new installations and (B) for existing ones.
Section 250.140(A) requires that all new circuits supplying these appliances include an EGC. These appliances must be grounded using the methods in 250.134 or 250.138. As a result, 3-wire cords are no longer permitted for new installations. Instead, a 4-wire cord must be used—hot, hot, neutral, and ground. When switching from a 3-wire to a 4-wire cord, the factory-installed bonding jumper between the neutral terminal and the metal frame must be removed. Failure to do this creates a direct connection between the neutral and the appliance frame, which violates code and will cause nuisance tripping of GFCI breakers, now required on many of these circuits under 210.8.
Section 250.140(B) applies only to existing branch circuits that do not have an equipment grounding conductor. In those cases, the grounded (neutral) conductor may be used to bond the metal frame of the appliance, but only if all of the following conditions are met:
In short, new appliance installations must use a 4-wire setup with a dedicated EGC, and the neutral-to-frame bond must be removed to avoid code violations and electrical hazards. The use of a 3-wire cord and bonding jumper is permitted only on compliant, pre-existing branch circuits that meet all the strict conditions in 250.140(B).

The 2023 NEC reorganized and clarified Section 250.140, which governs how the frames of electric ranges, ovens, cooking units, and clothes dryers must be grounded. In the 2020 NEC, this section included an exception allowing the use of the grounded (neutral) conductor for bonding the frame on existing branch circuits without an equipment grounding conductor (EGC). That structure was replaced in 2023 with two subsections: (A) for new installations and (B) for existing ones.
Section 250.140(A) requires that all new circuits supplying these appliances include an EGC. These appliances must be grounded using the methods in 250.134 or 250.138. As a result, 3-wire cords are no longer permitted for new installations. Instead, a 4-wire cord must be used—hot, hot, neutral, and ground. When switching from a 3-wire to a 4-wire cord, the factory-installed bonding jumper between the neutral terminal and the metal frame must be removed. Failure to do this creates a direct connection between the neutral and the appliance frame, which violates code and will cause nuisance tripping of GFCI breakers, now required on many of these circuits under 210.8.
Section 250.140(B) applies only to existing branch circuits that do not have an equipment grounding conductor. In those cases, the grounded (neutral) conductor may be used to bond the metal frame of the appliance, but only if all of the following conditions are met:
- The circuit is 120/240V single-phase 3-wire, or 208Y/120V from a 3-phase, 4-wire wye system.
- The grounded conductor is at least 10 AWG copper, 8 AWG aluminum, or copper-clad aluminum (added in 2023).
- The grounding contacts of any receptacles furnished as part of the appliance are bonded to the frame.
- The grounded conductor is insulated, or uninsulated only if it's part of Type SE cable that originates at the service equipment.
- If the SE cable originates at equipment other than the service, the grounded conductor must be insulated or field-covered using listed insulating material, like sleeving or tape, inside the supply enclosure.
In short, new appliance installations must use a 4-wire setup with a dedicated EGC, and the neutral-to-frame bond must be removed to avoid code violations and electrical hazards. The use of a 3-wire cord and bonding jumper is permitted only on compliant, pre-existing branch circuits that meet all the strict conditions in 250.140(B).