Hi
I'm working on a small apartment project, about a dozen units, 3 stories, type VB construction, new construction. The owner would really like to have no ceilings leave structure and ductwork exposed and paint out. Not that it relates to the question (I think), but we have a small-ish retail space on part of the ground floor. We also have a small rooftop amenity. We are under the Ohio Building Code which follows the 2015 IBC mostly.
We have a type 13 sprinkler system throughout, so per Section 711 I can have 1/2 hour only between dwelling units, per the exception in 711.2.4.3. And per 711.2 exception 2 the supporting structure does not have to be protected for type VB construction. I take this to mean i could, in theory, have the full fire rating in the floor assembly above the trusses.
However, so far as I've been able to find, there is no tested UL assembly for 1/2 hr with exposed wood trusses below, tried the UL Directory, USG Design Studio and other resources.
So, I've been looking at either the prescriptive (section 721) or calculated (section 722).
In 721, the closest I see is Item 13, double wood floor over joists (as a side note, this includes asbestos paper. I would assume that I cannot use open web wood trusses in this scenario. Anyway, all these options still have plaster or gwb ceilings - which I would also assume rules out putting this layer on top of the structure.
The sections I see with "none" listed under ceiling construction are lightweight concrete on steel deck - so does not apply.
I do see item 21 which has wood trusses, but unless i can put the gwb "ceiling" on top of the structure, that doesn't work either.
So, I ruled this approach out.
Then I looked at section 722. The wood section there 722. 6. 722.6.2.1 tells me that if I use a membrane it has to be on the exposed side - not clear if this rules out any possibility of putting the membrane on top, between the structure and the floor assembly. If so, would kind of knock this approach out too. 722.6.2.4 tells me that I have to have a regular wood subfloor and finish floor (which we'd have) or I can use any membrane in 722.6.2 [1] as long as it's more than 15 minutes. However, it also says, in Note a, that this only applies to joists, not trusses. Could I use TJIs with 1 layer of type X GWB (40 min per 722.6.2 [1] in between the joists, say screwed to the underside of the subfloor? If not, do I have any other options here?
The only other thing I can see is 722.1 tells me I could calculate based on a Wood Association manual. I don't have this, is this likely to provide a solution?
So with all this, ultimately my question is, is there any way to do a 1/2 hr wood truss floor assembly with exposed structure / no ceiling?
Thanks, Eric
I'm working on a small apartment project, about a dozen units, 3 stories, type VB construction, new construction. The owner would really like to have no ceilings leave structure and ductwork exposed and paint out. Not that it relates to the question (I think), but we have a small-ish retail space on part of the ground floor. We also have a small rooftop amenity. We are under the Ohio Building Code which follows the 2015 IBC mostly.
We have a type 13 sprinkler system throughout, so per Section 711 I can have 1/2 hour only between dwelling units, per the exception in 711.2.4.3. And per 711.2 exception 2 the supporting structure does not have to be protected for type VB construction. I take this to mean i could, in theory, have the full fire rating in the floor assembly above the trusses.
However, so far as I've been able to find, there is no tested UL assembly for 1/2 hr with exposed wood trusses below, tried the UL Directory, USG Design Studio and other resources.
So, I've been looking at either the prescriptive (section 721) or calculated (section 722).
In 721, the closest I see is Item 13, double wood floor over joists (as a side note, this includes asbestos paper. I would assume that I cannot use open web wood trusses in this scenario. Anyway, all these options still have plaster or gwb ceilings - which I would also assume rules out putting this layer on top of the structure.
The sections I see with "none" listed under ceiling construction are lightweight concrete on steel deck - so does not apply.
I do see item 21 which has wood trusses, but unless i can put the gwb "ceiling" on top of the structure, that doesn't work either.
So, I ruled this approach out.
Then I looked at section 722. The wood section there 722. 6. 722.6.2.1 tells me that if I use a membrane it has to be on the exposed side - not clear if this rules out any possibility of putting the membrane on top, between the structure and the floor assembly. If so, would kind of knock this approach out too. 722.6.2.4 tells me that I have to have a regular wood subfloor and finish floor (which we'd have) or I can use any membrane in 722.6.2 [1] as long as it's more than 15 minutes. However, it also says, in Note a, that this only applies to joists, not trusses. Could I use TJIs with 1 layer of type X GWB (40 min per 722.6.2 [1] in between the joists, say screwed to the underside of the subfloor? If not, do I have any other options here?
The only other thing I can see is 722.1 tells me I could calculate based on a Wood Association manual. I don't have this, is this likely to provide a solution?
So with all this, ultimately my question is, is there any way to do a 1/2 hr wood truss floor assembly with exposed structure / no ceiling?
Thanks, Eric