Rated opening within 10 feet of stairway
Lincoln
You can say that I am being lazy because I should simply drive across town and look up the answer myself within my code book.
Applicable code: 2009 IBC
New exterior (outdoor) stairway off the second floor to fix the fact that the contractor slipped in a second floor where the plans did not call for a second floor but only a small mezzanine requiring only one enclosed (interior) stairway.
The solution is to provide a second exit which is within 10 feet of the window directly below the stair landing. My experience is that the window is replaced with wire glass and we can then move on to solve the next problem. Okay... please remind me of the code section that includes the 10 ft. rule.
Feel free to say that I am being lazy.
Thanks
1022.6 Exit enclosure exterior walls. Exterior walls of an exit enclosure shall comply with the requirements of Section 705 for exterior walls. Where nonrated walls or unprotected openings enclose the exterior of the stairway and the walls or openings are exposed by other parts of the building at an angle of less than 180 degrees (3.14 rad), the building exterior walls within 10 feet (3048 mm) horizontally of a nonrated wall or unprotected opening shall have a fire-resistance rating of not less than 1 hour. Openings within such exterior walls shall be protected by opening protectives having a fire protection rating of not less than 3/4 hour. This construction shall extend vertically from the ground to a point 10 feet (3048 mm) above the topmost landing of the stairway or to the roof line, whichever is lower.
This section does not require exterior walls of a stairway enclosure to have the same fire-resistance rating as interior walls; however, to minimize the potential fire spread into the stairway from the exterior, the issue of the exterior wall of the stairway and adjacent exterior walls of the building is addressed. Essentially, there are two alternatives where an exposure hazard exists: either (1) provide protection to the stairway by having a fire-resistance rating on its exterior wall or (2) provide a fire-resistance rating to the walls adjacent to the stairway. The ratings apply for a distance of 10 feet (3048 mm) measured horizontally and vertically from the stairway enclosure where those walls are at an angle of less than 180 degrees (3.14 rad) from the enclosure's exterior wall [see Condition 1 in Figure 1022.6(1)]. When the adjacent exterior wall is protected in lieu of the stairway enclosure wall, the protection is to extend from the ground to a level of 10 feet (3048 mm) above the highest landing of the stairway. However, the protection is not required to extend beyond the normal roof line of the building.
The 180-degree (3.14 rad) angle criteria is based on the scenario where the exterior wall of the stair enclosure is in the same plane and flush with the exterior wall of the building [see Conditions 2 and 3 in Figure 1022.6(1)]. In this scenario, a fire would need to travel 180 degrees (3.14 rad) around in order to impinge on the stair. Based on studies of existing buildings, this 180-degree (3.14 rad) spread of fire does not appear to be a problem. This criteria is only applicable when the angle between the walls is 180 degrees (3.14 rad) or less.
As the fire exposure on the exterior is different than can be expected on the interior, the fire-resistance rating of the exterior wall is not required to exceed 1 hour, regardless of whether it is the stairway enclosure wall or the adjacent exterior wall, unless the exterior wall is required by other sections of the code to have a higher fire-resistance rating. The fire protection rating on any openings in the exterior wall of a stairway enclosure or adjacent exterior wall within 180 degrees (3.14 rad) is to be a minimum of 3/4 hour [see Figure 1022.6(2)].
In a situation where the upper levels are smaller than lower levels, an interior stairway can end up having an exterior wall when it moves above the roof of the lower levels. In this situation, the question is the rating requirements for the exterior wall of the stairway over the roof. Therefore, the exterior wall of the stairway must meet the vertical opening provisions in Section 705.8.6.
You do know it is Saturday and requires time and a half pay.
No wire glass please