As it is a level 1 alteration....
SECTION 703
FIRE PROTECTION
703.1 General. Alterations shall be done in a manner that maintains the level of fire protection provided.
If it were level 2:
805.5 Openings in corridor walls. Openings in corridor
walls in any work area shall comply with Sections 805.5.1
through 805.5.4.
Exception: Openings in corridors where such corridors
are not required to be rated in accordance with the International
Building Code.
805.5.1 Corridor doors. Corridor doors in the work area
shall not be constructed of hollow core wood and shall not
contain louvers. All dwelling unit or sleeping unit corridor
doors in work areas in buildings of Groups R-1, R-2, and
I-1 shall be at least 13/8-inch (35 mm) solid core wood or
approved equivalent and shall not have any glass panels,
other than approved wired glass or other approved glazing
material in metal frames. All dwelling unit or sleeping unit
corridor doors in work areas in buildings of Groups R-1,
R-2, and I-1 shall be equipped with approved door closers.
All replacement doors shall be 13/4-inch (44 mm) solid
bonded wood core or approved equivalent, unless the
existing frame will accommodate only a 13/8-inch (35 mm)
door.
Exceptions:
1. Corridor doors within a dwelling unit or sleeping
unit.
2. Existing doors meeting the requirements of
Guidelines on Fire Ratings of Archaic Materials
and Assemblies (IEBC Resource A) for a rating
of 15 minutes or more shall be accepted as meeting
the provisions of this requirement.
3. Existing doors in buildings protected throughout
with an approved automatic sprinkler system
shall be required only to resist smoke, be reasonably
tight fitting, and shall not contain louvers.
4. In group homes with a maximum of 15 occupants
and that are protected with an approved automatic
detection system, closing devices may be
omitted.
5. Door assemblies having a fire protection rating of
at least 20 minutes.