• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Recalled fire sprinkler heads

cda

Sawhorse 123
Joined
Oct 19, 2009
Messages
20,963
Location
Basement
So what do you do when you somehow find out a building has recalled heads in it???
 
Notify them in writing that all the heads are required to be replaced. usually, i'll find a copy of the CPSC or other documentation to substantiate. Then when they ask, who pays for it, I say it's up to the building owner.

I'd imagine that if they've had the same sprinkler company since the recall that they could be held accountable since 25 requires them to check for recalled heads.

5.2.1.1.6 Sprinklers that are subject to recall shall be replaced

per the manufacturer’s requirements.
 
Marshal Chris said:
Notify them in writing that all the heads are required to be replaced. usually, i'll find a copy of the CPSC or other documentation to substantiate. Then when they ask, who pays for it, I say it's up to the building owner. I'd imagine that if they've had the same sprinkler company since the recall that they could be held accountable since 25 requires them to check for recalled heads.

5.2.1.1.6 Sprinklers that are subject to recall shall be replaced

per the manufacturer’s requirements.
If the owner refused to participate in the recall, the service agency is not accounable. We have had 4 facilities refuse to take advantage of the recalls. Two did have us replace the heads, but only after the recall was ended. One facility paid us $40,000.00 to do what could have been done for free. They ignored 12 years of service reports. Two facilities have not had the heads replaced. They get written up at each inspection. Unlike the majority of you, we have no enforcement authority
 
They ignored 12 years of service reports. Two facilities have not had the heads replaced. They get written up at each inspection. Unlike the majority of you, we have no enforcement authority
Somebody with authority should be getting copies of your reports and follow up on the required corrections. That's part of my job. It usually just takes a phone call to the owner or maitnance supervisor to get the ball rolling
 
This comes from 02 version of 25. There is no language in standard itself, just the appendix.

A.4.1.4 Recalled products should be replaced or remedied.Such replacement or remedial product should be installed in

accordance with the manufacturer’s instructions and the appropriate

NFPA installation standards. A recalled product is a

product subject to a statute or administrative regulation specifically

requiring the manufacturer, importer, distributor,

wholesaler, or retailer of a product, or any combination of

such entities, to recall the product, or a product voluntarily

recalled by a combination of such entities.
And then this shows up in the 08 version:

5.2.1.1.6 Sprinklers that are subject to recall shall be replacedper the manufacturer’s requirements.
Fireguy, I agree with your statements, I was saying that the sprinkler company may be liable if they had no record of advising the building owner.
 
Anyone have the 05 version?

never mind I see that it jumped from 02 to 08
 
Last edited by a moderator:
Marshal Chris said:
Fireguy, I agree with your statements, I was saying that the sprinkler company may be liable if they had no record of advising the building owner.
I know some of will not believe this, but some jurisdictions see no value in inspections or service work of any kind. And we work in areas that an AHJ who tries to enforce codes, gets to speak to the city mgr about being a team player and how business needs to make a profit, and when was the last time a furniture store/school/ALF/anything actually burned. If an inspection results in problems, we do send service reports to management. After a couple of months of no action, I send reports to the AHJ. Fortunatly, my company is in a position of being busy taking care of those who think life safety is important. For those who do not get serious problems fixed, I have the option of firing them and letting them make other arrangements. And my techs have the same crappy attitude.
 
Thank goodness not all Fireguy!

Regarding recall items; in my opinion they are required to be noted on the inspection reports from the facility's service provider just like items including but not limited to......changes in storage comodities or operations that affect the existing protection scheme. In places with limited manpower, one can't be everywhere and that's why the code references are written that way. When the service provider needs, they know how to use us as we know how to use them.
 
If the recalled heads are noted on the report (which they should be), we require them to be replaced. We gernerally inspect frequently enough to force the issue before a recall has ended, and the service providers know to get us involved if they have someone ignoring them. The biggest problem we have faced recently is when they change service providers, the new tech finds something the old one either didn't find or ignored, and the recall has ended. That puts the owner in a rough spot. In those cases, we will work with the owner, within reason (within reason means the fire marshal approves a timeline - not me!).
 