righter101 brought up a question about shallow balconies in the Commercial Building Forum. I have a similar situation with regards to receptacle placement.
The 2011 NEC has revised Section 210.52 (E) (3) and removed the 20 sq. ft. exception for balconies, decks and porches. In other words, all balconies, decks and porches that are accessible from inside a dwelling unit require a receptacle.
I am reviewing a 5-story apartment building which has about 100 of these shallow balconies. They extend out from the building 8". We sometimes call them "juliette balconies" around here. Our Electrical Inspector Supervisor contends that receptacles are required.
I tend to disagree, however, IBC Section 1602 (2006) defines a balcony as "An exterior floor projecting from and supported by a structure without additional independent supports."
It's hard to not agree that this is a floor projection, even though it is only projecting 8". I just don't feel right about requiring these receptacles that would, basically be unusable except, maybe for Christmas lights on the guard rail.
Any thoughts?
GPE
The 2011 NEC has revised Section 210.52 (E) (3) and removed the 20 sq. ft. exception for balconies, decks and porches. In other words, all balconies, decks and porches that are accessible from inside a dwelling unit require a receptacle.
I am reviewing a 5-story apartment building which has about 100 of these shallow balconies. They extend out from the building 8". We sometimes call them "juliette balconies" around here. Our Electrical Inspector Supervisor contends that receptacles are required.
I tend to disagree, however, IBC Section 1602 (2006) defines a balcony as "An exterior floor projecting from and supported by a structure without additional independent supports."
It's hard to not agree that this is a floor projection, even though it is only projecting 8". I just don't feel right about requiring these receptacles that would, basically be unusable except, maybe for Christmas lights on the guard rail.
Any thoughts?
GPE