Buelligan
REGISTERED
2015 IRC
310.2.5 Replacement Windows Replacement windows installed in buildings meeting the scope of this code shall be exempt from the maximum sill height requirements of sections R310.1 and Sections R310.2.1 and 310.2.2 provided the replacement window meets the following conditions:
So based on this language "The replacement window is of the same operating style as the existing window". The replacement window can reduce the opening any amount as long as it is the same "operating style" (i.e. double hung for double hung). Although a change in style (i.e. double hung to single hung) must be equal or greater?
The situation is this. We had an existing condition (double hung) with a 24" of vertical opening (which is code minimum) to a replacement window (double hung) that only opens 17"! So the intent is to allow the emergency egress to be significantly reduced if the same style is used but the opening must remain the same just for changing the style?
Seems to me that not allowing ANY reduction in emergency egress would be the intent for all situations not just a style change. I realize that putting a replacement window inside the frame of the existing IS GOING TO reduce the opening, but a 7" reduction is pretty significant, right?
Example of what we are seeing:
Double Hung for Double Hung replacements:
Existing conditions: 24"x31" existing opening = 5.1 sq ft. (not 5.7 as required)
Replacement window: 17"x29" opening = 3.4 sq. ft!!!
So they can lose 7" of vertical opening and reduce it 1.7 sq.ft. just because it was the same style? But have to meet 5.7 if they change the style? Seems like replacement window industry logic and not code safety logic to me. But hey maybe I'm just being to cynical?
How do the rest of you read, interpret and enforce this?
310.2.5 Replacement Windows Replacement windows installed in buildings meeting the scope of this code shall be exempt from the maximum sill height requirements of sections R310.1 and Sections R310.2.1 and 310.2.2 provided the replacement window meets the following conditions:
1. The replacement window is the manufacturer's largest standard size window that will fit within the existing frame or existing rough opening. The replacement window is of the same operating style as the existing window or a style that provides for an equal or greater window opening area than the existing window.
2. Not a change......
2. Not a change......
So based on this language "The replacement window is of the same operating style as the existing window". The replacement window can reduce the opening any amount as long as it is the same "operating style" (i.e. double hung for double hung). Although a change in style (i.e. double hung to single hung) must be equal or greater?
The situation is this. We had an existing condition (double hung) with a 24" of vertical opening (which is code minimum) to a replacement window (double hung) that only opens 17"! So the intent is to allow the emergency egress to be significantly reduced if the same style is used but the opening must remain the same just for changing the style?
Seems to me that not allowing ANY reduction in emergency egress would be the intent for all situations not just a style change. I realize that putting a replacement window inside the frame of the existing IS GOING TO reduce the opening, but a 7" reduction is pretty significant, right?
Example of what we are seeing:
Double Hung for Double Hung replacements:
Existing conditions: 24"x31" existing opening = 5.1 sq ft. (not 5.7 as required)
Replacement window: 17"x29" opening = 3.4 sq. ft!!!
So they can lose 7" of vertical opening and reduce it 1.7 sq.ft. just because it was the same style? But have to meet 5.7 if they change the style? Seems like replacement window industry logic and not code safety logic to me. But hey maybe I'm just being to cynical?
How do the rest of you read, interpret and enforce this?