So they don't need accessible benches ever anywhere? I'm a plan reviewer/inspector. Only care about building code not ADASAD or ADA.
And they don't need a clear space in front of the locker, only an accessible route to it?
If you want to be sued
Assuming it is in PA
Building Code 2015 of Pennsylvania
1102.1 Design
Buildings and facilities shall be designed and constructed to be accessible in accordance with this code and ICC A117.1.
1109.9 Storage
Where fixed or built-in storage elements such as cabinets, coat hooks, shelves, medicine cabinets,
lockers, closets and drawers are provided in required accessible spaces, at least 5 percent, but not less than one of each type shall be accessible.
1109.12.1 Dressing, fitting and locker rooms
Where dressing rooms, fitting rooms or
locker rooms are provided, at least 5 percent, but not less than one, of each type of use in each cluster provided shall be accessible.
ICC A117.1
803.4 Benches. A bench complying with Section 903
shall be provided within the room.
903.1 General. Accessible benches shall comply with Section 903. 903.2 Clear Floor Space. A
clear floor space complying with Section 305, positioned for parallel approach to I the bench seat, shall be provided. 903.3 Size. Benches shall have seats 42 inches minimum in length, and 20 inches minimum and 24 inches maximum in depth