Residential Exception for Stair Enclosure Removed?!

InsideOut

REGISTERED
Joined
May 11, 2018
Messages
6
Location
Massachusetts
In IBC 2009 there was a long list of exceptions to the Exit requirements in 1022, but in IBC 2015 they are ALL removed. This is so confusing - they can't be requiring stairs inside a single residential dwelling unit to be 1-hour rated with fire doors and all, but that's what's implied. Can someone please tell me what I'm missing? Thanks!


Exceptions under 1022 in IBC 2009:

1. In all occupancies, other than Group H and I occupancies, a stairway is not required to be enclosed when the stairway serves an occupant load of less than 10 and the stairway complies with either Item 1.1 or 1.2. In all cases, the maximum number of connecting open stories shall not exceed two.

1.1. The stairway is open to not more than one story above its level of exit discharge; or

1.2. The stairway is open to not more than one story below its level of exit discharge.

2. Exits in buildings of Group A-5 where all portions of the means of egress are essentially open to the outside need not be enclosed.

3. Stairways serving and contained within a single residential dwelling unit or sleeping unit in Group R-1, R-2 or R-3 occupancies are not required to be enclosed.

4. Stairways in open parking structures that serve only the parking structure are not required to be enclosed.

5. Stairways in Group I-3 occupancies, as provided for in Section 408.3.8, are not required to be enclosed.

6. Means of egress stairways as required by Sections 410.5.3 and 1015.6.1 are not required to be enclosed.

7. Means of egress stairways from balconies, galleries or press boxes as provided for in Section 1028.5.1 are not required to be enclosed.
 
I think I just answered my own question - It looks like all of the exceptions were moved to different areas of the code. Exception 3 is now :
712.1.2 Individual Dwelling Unit
Unconcealed vertical openings totally within an individual residential dwelling unit and connecting four stories or less shall be permitted.
 
Look at Section 1019.3, which specifically addresses stairs within a dwelling unit.
 