WARNING:In CA Fire suppression systems, including sprinklers, MUST be designed by a Professional Engineer or a licensend sprinkler contractor.

Maximum Distance from Wall: half (1/2) of the maximum distance between sprinkler heads.

Minimum of 4 inches from wall

Minimum Distance Between Sprinklers: typically 6'-0".

Distance from Ceiling: minimum 1", maximum 12" for unobstructed construction. The minimum 1" is typical; however, concealed, recessed, and flush sprinklers may be mounted less than 1" from the ceiling and shall be installed based on their listing..
 
What edition of 13 or 13R are you under???

Monday can give you the section number
 
cda said:
What edition of 13 or 13R are you under???Monday can give you the section number
2013 edition

8.5.3.3 Minimum Distance from Walls.

8.5.3.3.1 The minimum distance permitted between a sprinkler and the wall shall comply with the value indicated in the applicable section for each type or style of sprinkler.

8.5.3.3.2 The distance from the wall to the sprinkler shall be measured perpendicular to the wall.

8.6.3.3 Minimum Distances from Walls. Sprinklers shall be located a minimum of 4 in. (102 mm) from a wall.
 
marcm said:
Is there a minimum distance that code requires sprinklers have to be from interior walls?