We are currently updating our NEC code editions to the 2011 edition and are revisiting Section 210.52©, for similar areas, and whether or not it is reasonable to consider a kitchenette/bar counters in finished basements as a similar areas as defined. The following are two responses I received last time we visited this issue:
Code response #1: As for spacing I would consider it a "Similar Area" and it is intended to supplement the extension in theory of the kitchen type area. Now, I would not require GFCI but the required spacing is enforced because NEC 210.52© makes reference to the Similar Areas but in NEC 210.8(6) makes no reference other than to kitchens....so I would not require them to be GFCI protected however.
You still have to meet the requirements of 210.52©(1) - ©(5).
Code response # 2: There was a change from the 2005 and the 2008 code cycles in 210.52© where the words “pantries, breakfast rooms, and similar areas of dwelling units” was added.
This change would now address the Butler Station as outlined in your question as to the installation spacing requirements of the counter top.
As outlined in 210.8 only those receptacles over the kitchen counter top would require GFCI protection.
As outlined in 210.12 Arc-Fault would be required as the Butler Station is not part of the kitchen.
In my opinion, the requirement is for areas where counter-top spaces are likely to be used with counter-top appliances, and in my experience this very much applies to basement finish kitchenette/bars where families and friends commonly gather on weekends and holidays loading up these counter-tops with blenders, crock-pots, and other appliances. I have heard many arguments, mostly in favor of not requiring spacing and 20amp circuits. The most common reasons have usually been voiced in "this is the way it has always been done," but clearly the NEC has made some changes in the language that might suggest they are not intending to continue this way. Again this issue centers around the vagueness, or lack of definition, particularly the word "similar," and the intent of the code change versus the historical application of the code section.
Any thoughts or comments would be greatly appreciated. Thank you.
Code response #1: As for spacing I would consider it a "Similar Area" and it is intended to supplement the extension in theory of the kitchen type area. Now, I would not require GFCI but the required spacing is enforced because NEC 210.52© makes reference to the Similar Areas but in NEC 210.8(6) makes no reference other than to kitchens....so I would not require them to be GFCI protected however.
You still have to meet the requirements of 210.52©(1) - ©(5).
Code response # 2: There was a change from the 2005 and the 2008 code cycles in 210.52© where the words “pantries, breakfast rooms, and similar areas of dwelling units” was added.
This change would now address the Butler Station as outlined in your question as to the installation spacing requirements of the counter top.
As outlined in 210.8 only those receptacles over the kitchen counter top would require GFCI protection.
As outlined in 210.12 Arc-Fault would be required as the Butler Station is not part of the kitchen.
In my opinion, the requirement is for areas where counter-top spaces are likely to be used with counter-top appliances, and in my experience this very much applies to basement finish kitchenette/bars where families and friends commonly gather on weekends and holidays loading up these counter-tops with blenders, crock-pots, and other appliances. I have heard many arguments, mostly in favor of not requiring spacing and 20amp circuits. The most common reasons have usually been voiced in "this is the way it has always been done," but clearly the NEC has made some changes in the language that might suggest they are not intending to continue this way. Again this issue centers around the vagueness, or lack of definition, particularly the word "similar," and the intent of the code change versus the historical application of the code section.
Any thoughts or comments would be greatly appreciated. Thank you.