I thought I might have asked this question here before, but I can't find it. Sorry if this is a duplicate. A double-egress pair of doors is where one door swings in one direction and one door swings in the opposite direction. They are often found in cross-corridor situations, especially in hospitals.The question is - do any of you require the doors to be "right-hand", where the door on your right as you face the opening is the one that swings in the direction of egress? I have had one code official in the last 25+ years require a left-hand double-egress frame to be changed to right-hand on one of my projects, and it has come up again. Click on the graphic below to enlarge.
View attachment 2045
I can't find anything in the IBC or NFPA 101 that would require this, although there is a requirement in the National Building Code of Canada:3.3.1.11. Door Swing1) Except as permitted by Article 3.3.1.12., a door that opens into a corridor or other facility providing access to exit from a suite or room not located within a suiteshall swing on a vertical axis.2) Except as permitted by Article 3.3.1.12., a door that opens into a corridor or other facility providing access to exit from a room or suite that is used or intended for an occupant load more than 60 or for a high-hazard industrial occupancy shall swing in the direction of travel to the exit.3) Every door that divides a corridor that is not wholly contained within a suite shall swing on a vertical axis in the direction of travel to the exit.4) If a pair of doors is installed in a corridor that provides access to exit in both directions, the doors shall swing in opposite directions, with the door on the right hand side swinging in the direction of travel to the exit. View attachment 2045
/monthly_2014_04/572953f08a080_DoubleEgressPairs.png.33cddf16a864e7118de582747bb9a845.png
View attachment 2045
I can't find anything in the IBC or NFPA 101 that would require this, although there is a requirement in the National Building Code of Canada:3.3.1.11. Door Swing1) Except as permitted by Article 3.3.1.12., a door that opens into a corridor or other facility providing access to exit from a suite or room not located within a suiteshall swing on a vertical axis.2) Except as permitted by Article 3.3.1.12., a door that opens into a corridor or other facility providing access to exit from a room or suite that is used or intended for an occupant load more than 60 or for a high-hazard industrial occupancy shall swing in the direction of travel to the exit.3) Every door that divides a corridor that is not wholly contained within a suite shall swing on a vertical axis in the direction of travel to the exit.4) If a pair of doors is installed in a corridor that provides access to exit in both directions, the doors shall swing in opposite directions, with the door on the right hand side swinging in the direction of travel to the exit. View attachment 2045
/monthly_2014_04/572953f08a080_DoubleEgressPairs.png.33cddf16a864e7118de582747bb9a845.png