• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

RMC Underground 90's Attached to PVC Conduit

some pride in workmanship in the install, I usually see a bunch of sticks and assort pieces of EMT masquerading as pips holder.

Is this going to have a pad poured over it? is there and grounding method required for the equipment?

would not hurt to bond it
 
Ground it? or bond it? Typically "isolated" metal parts get a pass, but that may be different if it is service conductors or some other stuff...It will be grounded because it is buried in the ground....;)
 
250.80 Service raceways and enclosures
Exception: A metal elbow that is installed in an underground nonmetallic raceway and is isolated from possible contact by a min. cover of 18" to any part of the elbow shall not be required to be connected to the ground system conductor or grounding electrode conductor.

250.86 Other conductor enclosures and raceways
Exception No. 3: A metal elbow that is installed in an underground nonmetallic raceway and is isolated from possible contact by a min. cover of 18" to any part of the elbow shall not be required to be connected to the ground system conductor or grounding electrode conductor.
 