I am new here and excited to have found this forum!
So, I am a member of the design team for a 2-story, Type 2B pre-engineered steel building. We are having an issue with stair enclosure - specifically how to avoid penetrating the top of the enclosure with our roof purlins. Our Fire barrier walls run to underside of metal B deck. Configuration of stairs make it extremely difficult to head off roof purlins to avoid enclosure. Can we use the assembly I501 attached to the underside of roof purlins - essentially making our own rated ceiling assembly over the enclosure?
Thanks in advance!
Cheers
UL Design No. I501 [h=2] Unrestrained Assembly Rating - 1 Hr Load Restriction - Limited to the Dead Weight of the Assembly.[/h] [h=4][/h]
1.
Perimeter Channels —
Used to support steel studs at both ends of wall structure. Min. 6 in. deep with min. 2 in. legs and formed from min. No. 20 MSG galv. steel (0.0329 in. thick bare metal thickness). Perimeter channels attached to wall structure with fasteners spaced not greater than 24 in. O.C. at both the top and bottom of the vertical leg. Maximum clear span from vertical leg to vertical leg of the perimeter channels is 8 ft., 2-1/4 in.
2.
Steel Studs —
Min. 6 in. wide with min. 1-5/8 in. legs containing folded back flanges and formed from min. No. 20 MSG galv. steel (0.0329 in. thick bare metal thickness). Studs to be cut 1/2 in. to 3/4 in. less than the clear span between the vertical legs of the perimeter channels. Studs spaced a max. 16 in. O.C. At each end of the stud, the un-faced side shall be secured to the perimeter channel with one 1/2 in. long pan-head steel screw. Studs are used at each end of the horizontal barrier to terminate the assembly at the adjoining wall. These end studs shall be secured to the adjoining wall in the same manner as the perimeter channels (Item1).
3.
Steel Strap —
Min 4 in. wide formed from min. No. 20 MSG galv. Steel (0.0329 in. thick bare metal thickness). Secured perpendicular to the studs at the centerline of the span using two 1/2 in. long pan-head steel screws. Strips to overlap one full stud bay at splice locations. As an alternate to the steel strap, Perimeter Channels (Item 1) may be substituted and installed in the same manner as the steel straps. If a continuous piece is not used, the abutted legs are installed on each side of the centerline of the span and overlap one full stud bay.
4. Gypsum Board* —Three layers of nom. 5/8 in. thick, 46 to 54 in. wide, gypsum board installed with long dimension perpendicular to the steel studs. Base layer installed with end joints in adjacent rows staggered min. 32 in. Boards secured to studs and perimeter channels with 1-1/4 in. long Type S steel screws spaced max. 16 in. O.C. Middle layer installed with end joints in adjacent rows staggered min. 32 in. Boards secured to the studs and perimeter channels with 1-5/8 in. long Type S steel screws spaced max. 16 in. O.C. Middle layer joints staggered a min. 16 in. from base layer joints Face layer installed with end joints in adjacent rows staggered min. 32 in. Boards secured to the studs and perimeter channels with 2-1/4 in. long Type S steel screws spaced max. 12 in. O.C. Face layer joints staggered a min. 16 in. from middle layer joints.
I am new here and excited to have found this forum!
So, I am a member of the design team for a 2-story, Type 2B pre-engineered steel building. We are having an issue with stair enclosure - specifically how to avoid penetrating the top of the enclosure with our roof purlins. Our Fire barrier walls run to underside of metal B deck. Configuration of stairs make it extremely difficult to head off roof purlins to avoid enclosure. Can we use the assembly I501 attached to the underside of roof purlins - essentially making our own rated ceiling assembly over the enclosure?
Thanks in advance!
Cheers
UL Design No. I501 [h=2] Unrestrained Assembly Rating - 1 Hr Load Restriction - Limited to the Dead Weight of the Assembly.[/h] [h=4][/h]

1.
Perimeter Channels —
Used to support steel studs at both ends of wall structure. Min. 6 in. deep with min. 2 in. legs and formed from min. No. 20 MSG galv. steel (0.0329 in. thick bare metal thickness). Perimeter channels attached to wall structure with fasteners spaced not greater than 24 in. O.C. at both the top and bottom of the vertical leg. Maximum clear span from vertical leg to vertical leg of the perimeter channels is 8 ft., 2-1/4 in.
2.
Steel Studs —
Min. 6 in. wide with min. 1-5/8 in. legs containing folded back flanges and formed from min. No. 20 MSG galv. steel (0.0329 in. thick bare metal thickness). Studs to be cut 1/2 in. to 3/4 in. less than the clear span between the vertical legs of the perimeter channels. Studs spaced a max. 16 in. O.C. At each end of the stud, the un-faced side shall be secured to the perimeter channel with one 1/2 in. long pan-head steel screw. Studs are used at each end of the horizontal barrier to terminate the assembly at the adjoining wall. These end studs shall be secured to the adjoining wall in the same manner as the perimeter channels (Item1).
3.
Steel Strap —
Min 4 in. wide formed from min. No. 20 MSG galv. Steel (0.0329 in. thick bare metal thickness). Secured perpendicular to the studs at the centerline of the span using two 1/2 in. long pan-head steel screws. Strips to overlap one full stud bay at splice locations. As an alternate to the steel strap, Perimeter Channels (Item 1) may be substituted and installed in the same manner as the steel straps. If a continuous piece is not used, the abutted legs are installed on each side of the centerline of the span and overlap one full stud bay.
4. Gypsum Board* —Three layers of nom. 5/8 in. thick, 46 to 54 in. wide, gypsum board installed with long dimension perpendicular to the steel studs. Base layer installed with end joints in adjacent rows staggered min. 32 in. Boards secured to studs and perimeter channels with 1-1/4 in. long Type S steel screws spaced max. 16 in. O.C. Middle layer installed with end joints in adjacent rows staggered min. 32 in. Boards secured to the studs and perimeter channels with 1-5/8 in. long Type S steel screws spaced max. 16 in. O.C. Middle layer joints staggered a min. 16 in. from base layer joints Face layer installed with end joints in adjacent rows staggered min. 32 in. Boards secured to the studs and perimeter channels with 2-1/4 in. long Type S steel screws spaced max. 12 in. O.C. Face layer joints staggered a min. 16 in. from middle layer joints.