linnrg
Sawhorse
So I have a couple of new rooftop solar installations going onto Existing commercial
buildings. Both are planned to be grid tied including rapid shutdown. Each are
intended to be solidly attached to the roof tops. I have reviewed NEC 690 and
IFC 605. One project, a fish processing facility: Has probably 6 plumbing vents
and at least 4 B vents for unit heaters, one exhaust vent for the smokers, and one
large vent for the large water boiler (at least 12"). The proposal is to have panels
right up to the edge of the sidewalls, 3' paths at each endwall, 3' path at the ridge.
Building is a PEMB that is at least 16' at the sidewalls. The second is a typical
strip mall that includes plumbing vents, some b vents, 5 or 6 air handlers (each
with electrical disconnects) and one up draft exhaust fan (commercial kitchen). Roof
is a flat roof without parapets on three sides and a small parapet at the front, type
5 construction. Intent is to have the 3' path all the way around and some path due
to the locations of the equipment.
I have cited UPC 906 to possible extend any plumbing vents - is there any other
clearance requirement for them?
I have cited IMC 802 so that the chimney/vents may need to be extended to get
the 2' above anything within the ten foot horizontal.
I have cited IMC 306.1 for the appliance maintenance space.
I have cited NEC 110.26
So far it seems that they have met the access (per IFC)
Are the reviewers out there requiring a roof as-built to determine the possible
setbacks or clearances that may be necessary?
What would you cite if you had wood burning chimneys that need to have a
chimney sweep ever so often? What do you cite for roof drainage and overflow?
Hoping to get some answers today, because I will be out on a fishing trip the
rest of the week.
buildings. Both are planned to be grid tied including rapid shutdown. Each are
intended to be solidly attached to the roof tops. I have reviewed NEC 690 and
IFC 605. One project, a fish processing facility: Has probably 6 plumbing vents
and at least 4 B vents for unit heaters, one exhaust vent for the smokers, and one
large vent for the large water boiler (at least 12"). The proposal is to have panels
right up to the edge of the sidewalls, 3' paths at each endwall, 3' path at the ridge.
Building is a PEMB that is at least 16' at the sidewalls. The second is a typical
strip mall that includes plumbing vents, some b vents, 5 or 6 air handlers (each
with electrical disconnects) and one up draft exhaust fan (commercial kitchen). Roof
is a flat roof without parapets on three sides and a small parapet at the front, type
5 construction. Intent is to have the 3' path all the way around and some path due
to the locations of the equipment.
I have cited UPC 906 to possible extend any plumbing vents - is there any other
clearance requirement for them?
I have cited IMC 802 so that the chimney/vents may need to be extended to get
the 2' above anything within the ten foot horizontal.
I have cited IMC 306.1 for the appliance maintenance space.
I have cited NEC 110.26
So far it seems that they have met the access (per IFC)
Are the reviewers out there requiring a roof as-built to determine the possible
setbacks or clearances that may be necessary?
What would you cite if you had wood burning chimneys that need to have a
chimney sweep ever so often? What do you cite for roof drainage and overflow?
Hoping to get some answers today, because I will be out on a fishing trip the
rest of the week.