Francis Vineyard
REGISTERED
Do you "infer" the requirements for ramps to be the same as stairs from the exception one (1) to 2406.4.6?
2406.4.6 & 2406.4.7 my reading requires safety glazing at landings between ramps and stairs but not at the ramp slope and landings at the top and bottom of ramps. If it were not for mentioning ramps in the first exception to 2406.4.6 I would not be questioning the intent.
2406.4.6 Glazing adjacent to stairs and ramps. Glazing where the bottom exposed edge of the glazing is less than 60 inches above the plane of the adjacent walking surface of stairways, landings between flights of stairs, and ramps shall be considered a hazardous location.
Exceptions:
1. The side of a stairway, landing or ramp that has a guard complying with the provisions of Sections 1013 and 1607.8, and the plane of the glass is greater than 18 inches from the railing.
2. Glazing 36 inches or more measured horizontally from the walking surface.
2406.4.7 Glazing adjacent to the bottom stair landing.
Glazing adjacent to the landing at the bottom of a stairway where the glazing is less than 36 inches above the landing and within 60 inches horizontally of the bottom tread shall be considered a hazardous location.
Exception: Glazing that is protected by a guard complying with Sections 1013 and 1607.8 where the plane of the glass is greater than 18 inches from the guard.
2406.4.6 & 2406.4.7 my reading requires safety glazing at landings between ramps and stairs but not at the ramp slope and landings at the top and bottom of ramps. If it were not for mentioning ramps in the first exception to 2406.4.6 I would not be questioning the intent.
2406.4.6 Glazing adjacent to stairs and ramps. Glazing where the bottom exposed edge of the glazing is less than 60 inches above the plane of the adjacent walking surface of stairways, landings between flights of stairs, and ramps shall be considered a hazardous location.
Exceptions:
1. The side of a stairway, landing or ramp that has a guard complying with the provisions of Sections 1013 and 1607.8, and the plane of the glass is greater than 18 inches from the railing.
2. Glazing 36 inches or more measured horizontally from the walking surface.
2406.4.7 Glazing adjacent to the bottom stair landing.
Glazing adjacent to the landing at the bottom of a stairway where the glazing is less than 36 inches above the landing and within 60 inches horizontally of the bottom tread shall be considered a hazardous location.
Exception: Glazing that is protected by a guard complying with Sections 1013 and 1607.8 where the plane of the glass is greater than 18 inches from the guard.