Do windows at 3rd level (which have sill at 36" above finish floor) need to be safety glazing? What code section? It's implied in 2406.4.3 (but that's an exception to a 9 SF condition that smaller windows don't meet).
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
1. No. If less than 9 sq. ft., one of the four criteria is not met; thus, no safety glazing is required (Section 2406.4.3).,Level 3 bedroom egress windows (< 9 SF) occur where greater than 25’ above adjacent grade outside. Sills at Level 3 are 36” above finish floor.
- Are these windows required to have safety glazing? Code section?
- Are these windows required to have indoor ‘guard’ fall protection since sill is 36” but < 42” guard height requirement? Code section?
That seems odd. As soon as the inside pane disappears, the outside pane is then the inside pane and a violation. So I will have to disagree.then the outside lite of an insulated glazing unit (and only the outside lite) can be non-safety glazing. The inside lite must still be safety glazing.
If the inside panel is safety glazed then it won't break so there is no need for the outer pane to also be safety glazed.That seems odd. As soon as the inside pane disappears, the outside pane is then the inside pane and a violation. So I will have to disagree.
It breaks.If the inside panel is safety glazed then it won't break so there is no need for the outer pane to also be safety glazed.
If you hit a concrete masonry wall hard enough, it, too, will break.It breaks.
Yes, according to the IBC when the bottom edge of the glass is 25 feet or higher above a walking surface below.Is the inner pane a suitable guard for the outer pane?
No more arbitrary than a deck needing rails above 30”. Why not 28”. Or 32”.Twenty-five feet seems to be an arbitrary dimension. Why not ten feet?
A majority of the requirements in the code are arbitrary. I have been told (anecdotally) that the allowable building areas were initially made up without any detailed objective analysis. Code requirements have evolved since based on real-world events and more objective analysis. Some requirements have been fine-tuned to be less arbitrary and new arbitrary requirements have been added to possibly be fine-tuned in the future.Twenty-five feet seems to be an arbitrary dimension. Why not ten feet?
Regarding 2406.4.7, I agree that the exception to 2406.4.3 would not apply since the exception only addresses glazing under those conditions. Section 2406.4.7 is a more specific condition than the general conditions in Section 2406.4.3, and the more specific one takes precedence over the general (Section 102.1). I assume the exception was not applied to Section 2406.4.7 because a person moving down the stairs has more kinetic energy than a person walking laterally; thus, the impact is potentially greater for the person walking down the stairs.I think I am with ICE on the 2 panel thing.....Other than locations covered by 2406.4.3
It doesn't say the "exposed" panel or anything like that and I am not sure it qualifies as any of the exemptions as far as guards 2406.4.7/ walls 2406.4.2 or whatever else....Ron, any idea why they didn't carry that to other locations?
According to the building code, yes.Soooooo....When the outer pane shatters, by the time it falls 25' it's not a problem? Not sure why the height is a thing on that one...
In regards to the "large pane" section we are talking about....yes....I rarely actually see it so I haven't thought much about it before now....the 25' must because of stuff hitting it from the outside (rocks/ balls/ etc.)Would this mean that when they use the film that 3 M makes that they can use instead of tempered glass would also be required on the outside glass if less than 25" above grade?
3. Outboard panes in insulating glass units
and other multiple glazed panels where the
bottom edge of the glass is 25 feet (7620
mm) or more above grade, a roof, walking
surfaces or other horizontal [within 45
degrees (0.79 rad) of horizontal] surface
adjacent to the glass exterior.