• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Sanitary Tees On Back

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,087
Location
Somewhere Too Hot & Humid
Only one of these is a vent:

IMG_0309.JPG
 
Jar, A very large city adjacent to our jurisdiction allows san tees to be install like that if it is a 2" going into 3".

Tim, looks like they used the invisible purple primer!
 
globe trekker said:
What code section applies here? Thanks!
P3005.1 Changes in direction in drainage piping shall be made... in accordance with Table P3005.1

If you look at Table P3005.1, sanitary tees are prohibited for all vertical-to-horizontal (pictured) and horizontal-to-horizontal changes.
 
I can see the reason for not placing a sanitary tee on its back if serving a WC or food prep sink. My question will they work on their backs if serving a tub or bath lav? Just curious
 
In practicality probably will never be an issue. Code-wise the table applies to all drainage piping, whether it be draining from a wc, lav, sink or tub.
 
I agree with Tim on both points.

That is not to say that an illegal horizontal san tee is as good as the approved combinations for flow. The approved combinations of fittings are more likely to allow passage of solids, including hairballs and soapscum from shower/tub/lavatories.
 
The reason that the adjacent jurisdiction allows them is when the san tee is down from wc. They figure the wc will wash any sediment that may accumulate.
 
This kind of system using san tees on their back is also not approved in the UPC.

Also, the 90 at the turn that goes from vertical to horizontal is to be equivilent to (2) 45's or combo Y, 1/8 bend (per the UPC). Even a vent where below the flood rim is to be approved drainage fittings.

Of course the "S" trap is way wrong.
 
Ya'll's thinking that's ok, has me so ****ed I ain't even gonna coment!

DIRECTION OF FLOWWWWWWWWW!

Stop smoking that pot and read your codes while your sitting on the pot!

Uncle Bob
 
Last edited by a moderator:
Sorry UB I dind't mean to get you upset. Not having a plumbing background leaves me at a disadvantage sometimes when explaing a code requirement to a homeowner . Jobsavers answer about soapscum and hairballs was all the explanation I will need to give.
 
MLC,

Not at all; for none plumbing background inspectors; "all fittings must be installed in the direction of flow" is best remembered.

For plumbers there is no excuse, just shoot him; but, the one they use mostly is; " I didn't have the right fitting on the truck, and it's 12 miles to the shop."

:D

Uncle Bob
 
Last edited by a moderator:
UB: They other excuse is "my helper put that in an I didn't see it before you got here." The other one is to have no lights on in the basement. Then they say I didn't think you were going to craw up in the crawlspace!
 
It's amazing what you can find if you actually crawl into the back of a crawl space! Nice "S" trap. Kind of like seeing a sasquatch. I didn't think those things actually existed.
 
Soooo..While in the field if I remember a tee going verticle or a tee going horizontal to horizontal should make me TEED OFF, is a good way to remember a change in direction violation. Table P3005.1

If the plumber would have used a wye and a 45 he could plug the end, correct?