how close can I put a second building. I have a existing office 6000 sq. ft. , I would like to but a 5800 sq. ft. daycare, 11 ft. away. building code inspector says it must be 20
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Yes it is Pa. code, and yes it is on the same lot.how close can I put a second building. I have a existing office 6000 sq. ft. , I would like to but a 5800 sq. ft. daycare, 11 ft. away. building code inspector says it must be 20
Existing building is a office with a one hour fire rating and projected new building will be a daycare. thanks againDepends on the construction type of the existing building and the construction type of the proposed building. With that information, we can work from there.
maybe, Im not sure.I found a youtube video : two or more buildings on the same lot ,from the 2006 ibc book, explaining it. The code officer says it changed, but he cant show me where.Maybe you have a zoning/land use separation issue?
That really doesn't tell me much. Is it Type I (A or B), Type II (A or B), Type III (A or B), Type IV, or Type V (A or B)?Existing building is a office with a one hour fire rating and projected new building will be a daycare. thanks again
I can almost guarantee that the citation will be to Table 602, which requires a 10-foot fire separation distance between Type VB buildings with Group B, I, or E (depending on specific design features of the day care) and an imaginary line located between the buildings.Ask the nice inspector for the code section he is getting the 20 feet from
So you can study it and also post the section number here .
Thanks for the help, the existing building is a group B. The new building will be a group E.There is simply not enough information with this question to give a good answer. So many factors, so little facts.
They do not, because I was told it was less than 12000 sq. ft.BR2, real important, does either building have a fire sprinkler system?
Your engineer is partially correct--an imaginary line is required between the two buildings, but each building must be at least 10 feet from that line to have non-rated exterior walls. Based on the information provided, the inspector is correct.The code office is saying the imaginary line starts ten feet from the existing building, then you must be ten ft. from there. My engineer says the imaginary line is the existing building, then you must be ten ft. away.
Sorry. if you read everything you would have seen, I paid a professional engineer to do the drawings and submit them, where the discrepancy came in was in the code officers review, saying the new building must be 20 ft. away. I was not trying to waste anyones time. We are just starting the building, there were no citations issued.A registered design professional needs to be hired.
This forum is not here to help DIY'ers perform code analysis and design. The lack of answers to the simple questions above are at minimum necessary to begin answering your questions. Hire a professional who can answer these questions and provide a complete scope and plans that are code compliant.
Thank you Very much, guess I was hoping to save the additional footage for a road on the back side of the new building. Thanks again for your time.Your engineer is partially correct--an imaginary line is required between the two buildings, but each building must be at least 10 feet from that line to have non-rated exterior walls. Based on the information provided, the inspector is correct.
If you design the new day care with a 1-hour exterior wall that faces the other building, then you can locate your imaginary line 10 feet from the existing building and locate your new building 1 foot away from the imaginary line. However, there are some complications for the new building: (1) you cannot have any overhangs (you may be required to have parapets per Section 705.11), (2) no openings are permitted in that wall, and (3) the wall must be rated for fire exposure from both sides.
For the existing building, there may also be complications. The line can only be placed at the 10-foot distance from the existing building if the wall has no more than 15% of its area used for unprotected openings. If openings exceed 15% of the wall area, but less than 25%, then that imaginary line will have to be pushed out to 15 feet from the existing building. If openings exceed 25% but not more than 45% of the wall area, then the imaginary line must be moved out further to 20 feet. If the openings exceed 45% but not more than 70%, add another 5 feet for a total of 25 feet between the existing building and the imaginary line. Only at a 30-foot distance can you have unlimited, unprotected opening area for an exterior wall of a nonsprinklered building. If the walls of the existing building are in fact rated for 1 hour (per one of your previous emails), the 10-foot distance can be reduced, but you would still have to place the imaginary line based on the area of existing openings in the wall as previously explained.
If you have drawings you can share, that would help. Otherwise, all you will get is our best guess based on the information provided.