error404
Bronze Member
2003 IBC, ANSI 98, NFPA 09
Use Group: B- Business (new construction)
2 Stories building + Basement (no elevator): Ground floor is a show room and it's fully accessible. Second floor is employees only; with a cubicles area, a restroom, and some private offices (one with a non-accessible PWD).
Basement: Employee rec room with a kitchenette.
Basement and 2nd floor are less than 3,000 sq.ft. (each) and the total occupancy is 39 (less than 50)
Per Section 1009.1 (IBC):
Does that mean that my fire stair does not need to be accessible? .... that's how I read it, but I wanted to double check.
Use Group: B- Business (new construction)
2 Stories building + Basement (no elevator): Ground floor is a show room and it's fully accessible. Second floor is employees only; with a cubicles area, a restroom, and some private offices (one with a non-accessible PWD).
Basement: Employee rec room with a kitchenette.
Basement and 2nd floor are less than 3,000 sq.ft. (each) and the total occupancy is 39 (less than 50)
Per Section 1009.1 (IBC):
Our stairs are 4'-0" wide (not including handrails). So we comply, however... Do we need to comply with section 1007?Exceptions:1. Stairways serving an occupant load of 50 or less shall
have a width of not less than 36 inches (914 mm).
1103.2.3 Employee work areas. Spaces and elementswithin employee work areas shall only be required to comply
with Sections 907.9.1.2, 1007 and 1104.3.1 and shall be
designed and constructed so that individuals with disabili-
ties can approach, enter and exit the work area.Work areas,
or portions of work areas, that are less than 150 square feet
(14 m2) in area and elevated 7 inches (178 mm) or more
above the ground or finish floor where the elevation is essential
to the function of the space shall be exempt from all
requirements.
So it does needs to be accessible per 1007... however:1007.3 Enclosed exit stairways. An enclosed exit stairway, tobe considered part of an accessible means of egress, shall have
a clear width of 48 inches (1219 mm) minimum between handrails
and shall either incorporate an area of refuge within an enlarged
floor-level landing or shall be accessed from either an
area of refuge complying with Section 1007.6 or a horizontal
exit.
We are Group B, but the offices are not for health care providers.1104.4 Multilevel buildings and facilities. At least one accessibleroute shall connect each accessible level, including mezzanines,
in multilevel buildings and facilities.
Exceptions:
1. An accessible route is not required to stories and mezzanines
above and below accessible levels that have
an aggregate area of not more than 3,000 square feet
(278.7 m2). This exception shall not apply to:
1.1. Multiple tenant facilities of Group M occupancies
containing five or more tenant spaces;
1.2. Levels containing offices of health care providers
(Group B or I); or
1.3. Passenger transportation facilities and airports
(Group A-3 or B).
Does that mean that my fire stair does not need to be accessible? .... that's how I read it, but I wanted to double check.