603.1.11- Partitions dividing portions of stores, offices or similar places occupied by one tenant only and that do not establish a corridor serving an occupant load of 30 or more shall be permitted to be constructed of fire-retardant-treated wood, 1-hour fire-resistance-rated construction or of wood panels or similar light construction up to 6 feet (1829 mm) in height.
Read the last three items. "fire retardant wood, 1 hr........ OR ..........
isnt this 3 options as or statement?
1 .fire treated.....
2. 1 hour FRRC
3. OR wood panel up to 6'
?????????????????????????????????????????
code official is saying that it is 1 hour fire résistance rated construction that is built of fire retardant treated lumber OR wood panels or similiar...........
Can I build a partition that is a 1hr rated assembly that is not using fire retardant wood above 6'?
I know that the commentary seems to not support this but the use of the commas and the "or" seems confusing no????
Read the last three items. "fire retardant wood, 1 hr........ OR ..........
isnt this 3 options as or statement?
1 .fire treated.....
2. 1 hour FRRC
3. OR wood panel up to 6'
?????????????????????????????????????????
code official is saying that it is 1 hour fire résistance rated construction that is built of fire retardant treated lumber OR wood panels or similiar...........
Can I build a partition that is a 1hr rated assembly that is not using fire retardant wood above 6'?
I know that the commentary seems to not support this but the use of the commas and the "or" seems confusing no????