I need some assistance please!
From the 2006 IRC: Section 3603.4 ( and from Article 210.11©(3) from
the 2008 NEC ): Bathroom branch circuit.
"A minimum of one 20-ampere branch circuit shall be provided to supply
bathroom receptacle outlet(s). Such circuits shall have no other outlets.
Exception: Where the 20-ampere circuit supplies a single bathroom, outlets
for other equipment within the same bathroom shall be permitted to be
supplied in accordance with Section E3602."
As I understand this code section, it seems to be limiting the outlets
supplied to a particular bathroom, to ONLY that bathroom. However, I have
a Mike Holt Illustrated NEC Guide that is saying " it is ok to supply other
bathroom GFCI rated receptacles from one bathroom GFCI rated receptacle."
If the code section is saying "Such circuits shall have no other outlets", ...isn't
a receptacle in another bathroom an outlet in another room?
Can someone please cite some code section(s) to clarify this conundrum.
Thank you!
.
From the 2006 IRC: Section 3603.4 ( and from Article 210.11©(3) from
the 2008 NEC ): Bathroom branch circuit.
"A minimum of one 20-ampere branch circuit shall be provided to supply
bathroom receptacle outlet(s). Such circuits shall have no other outlets.
Exception: Where the 20-ampere circuit supplies a single bathroom, outlets
for other equipment within the same bathroom shall be permitted to be
supplied in accordance with Section E3602."
As I understand this code section, it seems to be limiting the outlets
supplied to a particular bathroom, to ONLY that bathroom. However, I have
a Mike Holt Illustrated NEC Guide that is saying " it is ok to supply other
bathroom GFCI rated receptacles from one bathroom GFCI rated receptacle."
If the code section is saying "Such circuits shall have no other outlets", ...isn't
a receptacle in another bathroom an outlet in another room?
Can someone please cite some code section(s) to clarify this conundrum.
Thank you!
.