• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Sections in the IEBC that all states should have

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,057
Location
Somewhere Too Hot & Humid
Let's start with this section that is in the FBC Existing but not in the IEBC:

302.6Swimming pools.​

The provisions of Sections 302.6.1 and 302.6.2 apply to all alterations, repairs, additions, and relocation of equipment at existing swimming pools regardless of compliance method.

302.6.1Ground-fault circuit-interrupter protection for personnel.​

Outlets supplying repaired, replaced, altered, or relocated pool pump motors connected to single-phase, 120-volt through 240-volt branch circuits, whether by receptacle or by direct connection, and outlets supplying all other repaired, replaced, altered, or relocated electrical equipment and underwater luminaires operating at voltages greater than the low voltage contact limit, connected to single-phase, 120-volt through 240-volt branch circuits, rated 15- and 20-amperes, whether by receptacle or by direct connection, shall be provided with ground-fault circuit interrupter protection for personnel.

302.6.2Equipotential bonding.​

Any of the parts specified in 680.26(B)(1) through (B)(7) of the NFPA 70, National Electrical Code that are repaired, replaced, altered, or installed new at an existing swimming pool shall be connected to the existing bonding system using solid copper conductors, insulated, covered, or bare, not smaller than 8 AWG or with rigid metal conduit of brass or other identified corrosion-resistant metal. Connections to bonded parts shall be made in accordance with Section 250.8 of NFPA 70, National Electrical Code. An 8 AWG or larger solid copper bonding conductor provided to reduce voltage gradients in the pool area shall not be required to be extended or attached to remote panelboards, service equipment, or electrodes. All metallic float-in light rings shall be connected to the equipotential bonding grid. Float-in light rings with no provision for bonding, and other devices which do not provide an electrical connection between a metallic underwater luminaire and the forming shell of a wet niche fixture, including screws or bolts not supplied by the luminaire’s manufacturer and listed for use with the specific luminaire, shall not be allowed for use with any underwater luminaire that is required to be grounded. Where none of the bonded parts is in direct connection with the pool water, the pool water shall be in direct contact with an approved corrosion-resistant conductive surface that exposes not less than 9 square inches (5800 mm2) of surface area to the pool water at all times. The conductive surface shall be located where it is not exposed to physical damage or dislodgement during usual pool activities, and it shall be bonded in accordance with Section 680.26(B) of the NFPA 70, National Electrical Code. A bonded concrete pool shell shall be considered to be a conductive surface. The interior metallic surface or surfaces of any forming shell (wet niche) shall not be covered with any material, including plaster, except potting compound covering internal bonding connections in conformance with Section 680.23(B)(2)(b) of NFPA 70, National Electrical Code, shall be allowed.
 