The alternative to this would be taking the MC cable on the right, bringing it back to the left side just to secure it then looping it back causing undue stress on the connection point and wasting cable. The cable tie in the middle is acting as a support.@ ~ @
By not enforcing the adopted requirement of the NEC, and specifically
Article 330.30(B), ...then a precedent would then be set........What
about the next time, and THERE WILL BE a next time, ...when the distance
is a little bit farther, and the next time when the distance is still even
farther away ?.......How many of us have heard the statement "Well you
didn't make me do it on the last job, why are you making me do it now" ?
Anyone who is a regular visitor or member on this Forum sees the direct
results of what happens when the various adopted Codes & Standards
are not enforced [ i.e. - please refer to the various pictures and
applications that **ICE** has ].
IMO, ...as an Inspector the non-compliant condition must be enforced to
the Code [ read Article ] as adopted by the jurisdiction.
@ ~ @
YesWill the ceiling be accessible?
330.30(D)(2)
Is it 12" as the pig flies or is it 12" of actual MC cable. Neither cable is 12" or less in actual cable and if it is as the pig flies then the cables could be infinitely long. So one cable is attached to another, however, the point is moot given the Code.My reaction was that with the cables being attached to one another, appears to immobilize them within the 12". JMHO
What if I told you this installation was under the 2017 NEC and that the cable ties were UL Type 21S? Would that change your opinion?
Wouldn't the MC require the metallic type approved 21's ties?
Have to be a wrapper laying on the floor for verification, cuz I can't tell one tie from another.
The alternative to this would be taking the MC cable on the right, bringing it back to the left side just to secure it then looping it back causing undue stress on the connection point and wasting cable. The cable tie in the middle is acting as a support.
What if I told you this installation was under the 2017 NEC and that the cable ties were UL Type 21S? Would that change your opinion?
I don't think a wire tie from a MC cable to another MC cable can be used for supporting:
300.11 (C) Cables not used as a means of support. Cable wiring methods shall not be used as a means of support for other cables, raceways, or non electrical equipment.
But if this is a whip it's ok for the first 6'.but not elsewhere.