Do any of you have experience with security interlocks (aka mantraps)? It's a series of two doors that creates a vestibule. Only one door can be opened at a time - either for security or to create an airlock leading to a clean room.
It can create an egress issue because if the outer door is held open, the inner door won't unlock to allow egress. I haven't been able to find any code language that addresses interlocks, but I see them quite often in lab areas and occasionally in retail (jewelry stores). Electromagnetic locks are typically used to create the interlock, but applying the access-controlled egress doors section of the code obviously defeats the purpose of the interlock.
There are things that can be done to make this application safer, like a) limit the use to certain occupancies, like a lab that is occupied by "trained traffic," b) unlock both doors upon fire alarm, c) provide an emergency override button inside the lab, d) in the case of a jewelry store, require a guard stationed at the door.
What's the protocol in your area and is there any code language to support it? I did a post about interlocks on my blog a while back, and a fire marshal just asked me a question so I thought I'd run it by you all. Here's a link to the post, which includes a video of how an interlock works: http://www.ihatehardware.com/2010/03/interlocks/
It can create an egress issue because if the outer door is held open, the inner door won't unlock to allow egress. I haven't been able to find any code language that addresses interlocks, but I see them quite often in lab areas and occasionally in retail (jewelry stores). Electromagnetic locks are typically used to create the interlock, but applying the access-controlled egress doors section of the code obviously defeats the purpose of the interlock.
There are things that can be done to make this application safer, like a) limit the use to certain occupancies, like a lab that is occupied by "trained traffic," b) unlock both doors upon fire alarm, c) provide an emergency override button inside the lab, d) in the case of a jewelry store, require a guard stationed at the door.
What's the protocol in your area and is there any code language to support it? I did a post about interlocks on my blog a while back, and a fire marshal just asked me a question so I thought I'd run it by you all. Here's a link to the post, which includes a video of how an interlock works: http://www.ihatehardware.com/2010/03/interlocks/