Could you provide the first number of the Section? It seems to me that there's plenty in Article 250 that could be used to deny this. But I know that you like to find a needle in stacks of needles.Hint: It’s not in 250
Oh? There's 250.8(A), which speak directly to this connection.This is not allowed per NEC?
OK, you did not fall for it. Yes, it is 250.8(A)Oh? There's 250.8(A), which speak directly to this connection.
Cheers, Wayne
And you have accused me of trolling.OK, you did not fall for it. Yes, it is 250.8(A)
Ehhh, not so much trolling as making people question whether or not they are right. It is a confidence building move.And you have accused me of trolling.
Correct and could.And just to clarify...that screw doesn't meet #6 or it would/ could be allowed
I don't follow this comment. The picture in the OP looks like a 4 square junction box or the like. NEC 314.40(B) requires such boxes to have a wall thickness of 1/16", unless listed. Are there listed boxes out there that are actually thinner, per the exception? If not, then a 32 tpi machine screw will provide the two threads required.No matter what screw is used, the sheet metal is too thin to get teo threads.