• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Separate Exhaust for Toilet Room

dchin

Member
Joined
Feb 20, 2010
Messages
15
I am working on a small 800 sf T.I. in a two-story office building in New Jersey, converting the space into a dental office. There is an existing toilet room exhaust fan (controlled by switch) that has a duct leading into a cmu shaft that leads to the roof. We are adding an exhaust fan for the lab area (also controlled by a switch) and an exhaust fan in the mechanical closet, controlled by a thermostat.

My mechanical engineer thinks that the two new exhaust fans cannot exhaust into the existing toilet room exhaust duct, but must be separate. IMC 401.4.1 is vague on this - " the exhaust from a bathroom or kitchen in a residential dwelling shall not be considered to be hazardous or noxious contaminant," so my engineer's thinking is that a commercial toilet exhaust would be hazardous.

The DCA official she spoke to said that there is a possibility that if the exhaust systems were combined, there is the possibility that the toilet exhaust could enter the other spaces if the other exhaust fans are 'OFF".

It will be a lot of work to install new exhaust ducts to the roof, and I would like to know if others have run into this situation. Could the exhausts for the two new fans at least be combined?

Thanks, - Donald
 
Re: Separate Exhaust for Toilet Room

architect

really odd, but when I type "Arch----t it comes out as "man with pencil who draw". Practical joke?

Donald
 
Re: Separate Exhaust for Toilet Room

A$rchitect always comes out at man who draws with pencil. Long standing inside joke. There is also one for persons who practice the law.
 
Re: Separate Exhaust for Toilet Room

It sounds like the condition you describe would allow the exhaust fan in one toilet room to push the air into the other toilet room if that fan were not running. This would not be within the intent of the code. A common fan would probably be OK. I also wonder if back draft dampers would address this concern.
 
Re: Separate Exhaust for Toilet Room

Three exhaust fans combining into a single exhaust will not work. The official you spoke with is correct except it's not a "possibility", it's a sure thing that exhaust will not all be exhaust out of the building.

A common inline exhaust fan with correct duct sizing should be okay (fan located after ducts are combined). This will probably still require new ducting to the exterior as the existing duct is probably not large enough.
 
Re: Separate Exhaust for Toilet Room

There is no prohibition against combining toilet exhaust with other exhausts, but the practical issue with forcing air from one exhaust into another is valid. The backdraft dampers on those fart fans are pretty useless.

"Hazardous" exhaust is defined in IMC 510. Toilet exhaust is not hazardous (not even my teenager's bathroom).

The code issue to be concerned with is 601.4 "Exhaust ducts under positive pressure, chimneys, and vents shall not extend into or pass through ducts or plenums." Is this space plenum return?
 
Re: Separate Exhaust for Toilet Room

Thanks for all your replies and advice. The space above the ceiling is not used as a plenum return.

Donald

p.s. lawyer - I had to try it out.
 